Comments on Draft Study Plan and February 26th, 2025 Stakeholder Meeting

2025-2026 Transmission planning process

Print
Comment period
Feb 26, 08:00 am - Mar 12, 05:00 pm
Submitting organizations
View by:

Bay Area Municipal Transmission Group (BAMx)
Submitted 03/12/2025, 02:17 pm

Submitted on behalf of
City of Palo Alto Utilities and City of Santa Clara dba Silicon Valley Power

Contact

Paulo Apolinario (papolinario@svpower.com)

1. Please provide your organization's comments on the draft Reliability Assessment

The Bay Area Municipal Transmission Group (BAMx)[1] appreciates the opportunity to comment on the California Independent System Operator (CAISO) Draft 2025-2026 Transmission Planning Process (TPP) Unified Planning Assumption and Study Plan (Draft Study Plan). The comments and questions below address the Study Plan posted on February 19, 2025, and discussed during the stakeholder meeting on February 26, 2025. We continue to see CAISO’s desire to work with Stakeholders to enhance each year’s plan. We look forward to working with the CAISO on this collaborative process.

Spring Off-Peak Scenario in Long-term Planning Horizon (2035)

In the previous 2024-2025 TPP cycle, the Spring Off-Peak base scenario studies were included in the Near-term Planning Horizon (5-year study). However, in the current 2025-2026 TPP cycle, the table on page 42[1] indicates that these studies have been shifted to the Long-term Planning Horizon year 2035. This significant change was not addressed in the stakeholder meeting on February 26, 2025, nor is it mentioned in the draft 2025-2026 Transmission Planning Process Unified Planning Assumptions and Study Plan[2] document.

BAMx recommends that CAISO provides additional context for the shift of the Spring Off-Peak base scenario study from the Near-term to the Long-term Planning Horizon.

 Grid-Enhancing Technologies (GETs) Consideration in Corrective Action Plans

During the stakeholder meeting on February 26, 2025, CAISO discussed the consideration of Grid Enhancing Technologies (GETs) when developing corrective action plans. The draft 2025-2026  Study Plan document on page 69 clarifies that these technologies may include “advanced conductors (high temperature, low sag characteristics), dynamic line ratings, power flow controllers, and topology optimizations”. However, the document does not clearly outline how CAISO evaluates GETs alternatives versus conventional transmission upgrades when developing Corrective Action Plans.

BAMx recommends that CAISO provides a detailed explanation of the process used to evaluate GETs alternatives in comparison to conventional transmission upgrades. Alternatively, CAISO could include an example of a GETs evaluation in the 2025-2026 Final Study Plan document to demonstrate how this evaluation is performed in practice.

 


[1] https://stakeholdercenter.caiso.com/InitiativeDocuments/2025-2026-TPP-SHMeeting1-DraftStudyPlan.pdf

[2] https://stakeholdercenter.caiso.com/InitiativeDocuments/2025-2026-Transmission-Planning-Process-Unified-Planning-Assumptions-and-Draft-Study-Plan.pdf


[1] BAMx consists of City of Palo Alto Utilities and City of Santa Clara, Silicon Valley Power.

2. Please provide your organization's comments on the draft Policy Assessment

Accounting for Gas Capacity Not Retained for Non-CPUC Jurisdictional

BAMx appreciates the CAISO staff’s efforts in incorporating non-CPUC jurisdictional integrated resource plans (IRP) in the analysis with the CPUC busbar mapped IRP base portfolio.[1] In cases where no CPUC portfolio is mapped to the same or nearby locations, the CAISO will transfer CPUC resources to locations that are behind the same constraints as the CPUC portfolio.[2] BAMx finds this approach to be reasonable. It appears that the non-CPUC-jurisdictional entities’ IRPs have cumulatively assumed retirement of gas capacity of 108 MW beginning in 2026 to 890 MW by 2045.[3] In the CPUC 2025-2026 TPP portfolios, the CPUC did not assume any new gas capacity that was not retained.[4] BAMx requests clarification on how the CAISO plans to adjust the remaining resource capacity in the CPUC portfolio to address the incremental non-CPUC-jurisdictional entities’ gas capacity that is not retained. In particular, please identify a combination of resource capacity by location that will be added to address the retirement of gas-fired capacity.

 


[1] CAISO Stakeholder Meeting Presentation, dated February 26, 2025, pp.69-71.

[2] Ibid, p. 70.

[3] Ibid, p. 71.

[4] Final busbar mapping dashboards for the base and sensitivity portfolios located at https://www.cpuc.ca.gov/industries-and-topics/electrical-energy/electric-power-procurement/long-term-procurement-planning/2024-26-irp-cycle-events-and-materials/assumptions-for-the-2025-2026-tpp

3. Please provide your organization's comments on the draft Economic Assessment

BAMx supports the stakeholder recommendation made during the February 26, 2025, meeting to hold additional one-off meetings on the Economic Assessment evaluation tools. These sessions could serve as a way to educate stakeholders on the specifics of how CAISO quantifies economic benefits for ratepayers using the Transmission Economic Assessment Methodology (TEAM).

4. Please provide your organization's comments on the draft Frequency Response Assessment

No comments at this time 

5. Please provide your organization's Economic Study Requests

No comments at this time 

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

No comments at this time 

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

No comments at this time 

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Electromagnetic Transient (EMT) Studies

BAMx encourages CAISO to continue the development of system-wide EMT models and incorporate these studies into the TPP. A comprehensive system-wide EMT model may provide a more accurate assessment of Inverter-Based Resources (IBRs) plant controls in the sub-transient time domain when evaluating primary and fast frequency response capabilities from IBRs. Developing these models may help identify any deficiencies not currently captured by traditional transient stability study methods when assessing frequency response.

BAMx Appreciates Commenting Opportunity

BAMx appreciates the opportunity to comment on the draft Study Plan. BAMx would also like to acknowledge the significant effort of the CAISO staff in developing the Study Plan to date and their willingness to work with the stakeholders. We plan to work with the CAISO staff to continue improving and enhancing the Study Plan.

California Community Choice Association
Submitted 03/12/2025, 03:46 pm

Contact

Shawn-Dai Linderman (shawndai@cal-cca.org)

1. Please provide your organization's comments on the draft Reliability Assessment

The California Community Choice Association (CalCCA) has no comments at this time.

2. Please provide your organization's comments on the draft Policy Assessment

CalCCA has no comments at this time.

3. Please provide your organization's comments on the draft Economic Assessment

CalCCA has no comments at this time.

4. Please provide your organization's comments on the draft Frequency Response Assessment

CalCCA has no comments at this time.

5. Please provide your organization's Economic Study Requests

CalCCA has no comments at this time.

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

CalCCA has no comments at this time.

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

CalCCA appreciates the opportunity to provide the California Independent System Operator (CAISO) with Transmission Planning Process and infrastructure-related policy concepts. As proposed in CalCCA’s comments to the CAISO’s Interconnection Process Enhancements (IPE) Track 3 Final Proposal,[1] the CAISO should consider the issue of energy-only (EO) resources seeking transmission plan deliverability (TPD) in the next IPE initiative. While the IPE Track 3 Final Proposal prohibits EO projects in Cluster 15 and later from ever seeking a TPD allocation, there are legitimate reasons why projects may pursue interconnection via the EO process, such as a willingness on the part of both developers and load-serving entities to contract for a period of time for EO deliveries. CalCCA, therefore, requests the CAISO reconsider preventing EO projects from ever seeking deliverability. Instead, the CAISO could explore allowing a project that enters the queue and comes online as EO to submit a new interconnection request and follow the intake and study process for obtaining deliverability. The IPE Track 3 Final Proposal states that the CAISO has considered the issue of EO resources seeking TPD, identified several policy issues that need to be discussed with stakeholders, and determined that the issue will need to be deferred to a future IPE initiative.[2] The CAISO should commit to considering EO resources seeking TPD in the next IPE initiative.  

 


[1]            CalCCA Comments on CAISO Interconnection Process Enhancements Track 3 Final Proposal (Mar. 4, 2025): https://stakeholdercenter.caiso.com/Comments/AllComments/45f69a3e-5151-4edb-9866-59b1511b1856#org-25d31bf5-e55d-45d2-b2b8-769846dcb3cb.

[2]            Id., at 26-27.

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

CalCCA has no additional comments at this time.

California Department of Water Resources
Submitted 03/05/2025, 05:08 pm

Contact

Corey Fong (Corey.Fong@water.ca.gov)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

The California Department of Water Resources (CDWR) thanks the California Independent System Operator (CAISO) for the opportunity to comment on the CAISO’s 2025-26 Transmission Planning Process (TPP).  CDWR was informed by Pacific Gas and Electric (PG&E) in 2024 that the PG&E owned 225 MVAR Capacitor Banks (CAP Banks) at the PG&E 230 kV Wheeler Substation are non-operational.  The base cases need to reflect that these CAP banks are out of service.

Background:

As CDWR was made aware by PG&E, the CAP banks cause voltage flickering above the 3% voltage deviation that is allowed with even only one step online because the steps are too large (three steps at 75 MVAR each) and PG&E has no current plan or ability for the CAP banks to be used currently. 

This issue is of concern to CDWR for a number of reasons.

  1. CDWR is the majority owner of 75% of the capacity on the Midway – Wheeler Ridge 230 kV transmission lines.
     
  2. The addition of the CAP banks was approved in the CAISO’s 2011-12 TPP as the "Wheeler Ridge Voltage Support1" project in which it was identified that there were voltage support issues on the Midway – Wheeler Ridge 230 kV transmission lines specifically at PG&E 230 kV Wheeler substation due to the large growth in PG&E’s radial sub-system there.
     
  3. A prolonged outage in 2024 caused a curtailment in CDWR’s capacity rights below CDWR's expected 75% capacity rights due to the same voltage support issues that should have been resolved by the use of the CAP banks. 
     
    1. These curtailments had economic impacts to CDWR requiring reduction of  energy scheduling by CDWR for critical water deliveries throughout California.
       
  4. To this day, all current and planning base cases (CAISO TPP/GIDAP & WECC) continue to include the CAP banks as operational whereas in reality, they have been inoperable basically since they first tried to come online. Since the units are modeled as operational, the actual system may not be as reliable in real-time.
     
  5. The CAP banks were a previously approved TPP project and eligible for recovery through the Transmission Access Charge (TAC).


CDWR understands that this is a unique circumstance and the implications of the continued use in modeling of a non-operational resource causes unknown impacts to existing planning processes and to system reliability.  CDWR would like CAISO to explore potential options to expedite and fix these issues, while also assuring that the issue is at least modeled and accounted for properly in current planning processes at all levels (CPUC/CEC/WECC etc).

 


1 "CAISO 2011-12 Wheeler Ridge Voltage Support Project" https://www.caiso.com/Documents/Decision_2011-12TransmissionPlan-Plan-MAR2012.pdf#page=140 

California Public Utilities Commission
Submitted 03/12/2025, 10:40 am

Contact

Katherine Stockton (katherine.stockton@cpuc.ca.gov) and Joshua Kim (Joshua.Kim@cpuc.ca.gov)

1. Please provide your organization's comments on the draft Reliability Assessment

Energy Division staff (Staff) of the California Public Utilities Commission (CPUC) develops and administers energy policy and programs to serve the public interest, advises the CPUC, and ensures compliance with CPUC decisions and statutory mandates. Staff provides objective and expert analyses that promote reliable, safe, and environmentally sound energy services at just and reasonable rates for the people of California.[1]  Further, Staff advocates on behalf of California ratepayers at the Federal Energy Regulatory Commission (FERC), under whose jurisdiction CAISO’s transmission planning falls. 

Staff appreciates this opportunity to ask clarifying questions on the Draft Reliability Assessment and the Draft Policy Assessment as part of CAISO’s 2025-2026 Transmission Planning Process (TPP) Unified Planning Assumptions and Draft Study Plan.[2] 

The Draft Reliability Assessment

The CAISO conducts reliability assessments annually to ensure that the transmission grid under CAISO’s control will meet or exceed reliability standards.[3] The assessments include power flow, transient stability, and voltage stability technical studies. The study horizon is both near-term (2027-2030) and long-term (2030-2040).[4] CAISO studies the PG&E Northern California (bulk) system, PG&E local areas, the SCE Southern California (bulk) system,[5] SCE local areas, the SDG&E area, the Valley Electric Association area, and the CAISO overall bulk system.[6]

The Reliability Assessment relies on the 2024 California Energy Demand Update (CEDU) Forecast 2024-2040 published by the California Energy Commission (CEC).  In the discussion of load forecasts in the February 26, 2025 stakeholder meeting, CAISO noted that new data center load forecasts have been moved from the "Other Adjustment" category and are now included as distinct load modifiers. This is new with the 2024 IEPR Update that was adopted on January 21, 2025.[7]

Staff requests that the CAISO study and report in the final Transmission Plan the load impact attributed to data centers and specify the number and scope of the TPP projects being proposed and approved because of this data center load.


[1] More information about the CPUC Energy Division is available at: https://www.cpuc.ca.gov/about-cpuc/divisions/energy-division

[2] Available at: https://stakeholdercenter.caiso.com/InitiativeDocuments/2025-2026-Transmission-Planning-Process-Unified-Planning-Assumptions-and-Draft-Study-Plan.pdf  

[3] The reliability assessment standards and criteria are discussed in Section 2.1, pp. 8-11 of  the draft study plan and include North American Electric Reliability Corporation (NERC) criteria and Western Electricity Coordinating Council (WECC) Regional Criteria.  

[4] The study horizon is covered in Section 2.2, p. 12 of the draft study plan and is based on the NERC TPL-001-5.1 Standard.

[5] CAISO also includes the SunZia and TransWest Express transmission lines that are under development in the Southern California (bulk) system. 

[6] The study areas are listed in Section 2.3, p. 13 of the draft study plan. 

[7] The 2024 IEPR CEDU update is comprised of updated tables that are available here under the “Forecast Files” header: https://www.energy.ca.gov/data-reports/reports/2024-integrated-energy-policy-report-update/2024-iepr-workshops-notices-and-0

2. Please provide your organization's comments on the draft Policy Assessment

The CAISO conducts policy assessments annually to “enable the CAISO to plan for and approve new transmission needed to support state or federal public policy requirements and directives,”[1] especially to plan for Renewable Portfolio Standard eligible resources that help the state achieve its greenhouse gas reduction goals.  During the Policy Assessment updates at the February 26, 2025 stakeholder meeting, the Public Advocates Office (Cal Advocates) asked about transmission upgrades on Slide 67 “2035 base portfolio transmission capability exceedances” of the CAISO’s presentation,[2] and in the CAISO’s August 2024 White Paper.[3]  Cal Advocates raised concerns that these transmission upgrades were not “right sized” and are potentially larger than needed to accommodate the interconnection queue. Staff understands that the CAISO considers more factors than just the interconnection queue in determining whether the upgrades evaluated are “right-sized,” and Staff reiterates its suggestions included in CAISO’s draft study plan:

CPUC staff encourage the CAISO to assess alternative and potentially less costly upgrades particularly for the exceedances discussed in the PD Modeling Assumptions Section 7 where the amount of resources behind the exceedances may not warrant the size and cost of the identified 2024 White Paper upgrades.[4]

Staff therefore requests more information on the CAISO’s efforts to contain costs, such as evaluating alternatives like Grid Enhancing Technologies.  Staff encourages consideration of Public Utilities Code § 345.5(b)(2), which directs CAISO to manage the transmission system in a manner consistent with, “Reducing, to the extent possible, overall economic cost to the state’s consumers.”

Additionally, Staff requests more information on what methodologies will be used to consider the impacts and potential approval of other alternatives like Grid Enhancing Technologies.


[1] CAISO’s draft study plan, p. 71. 

[2] CAISO’s presentation for the February 26, 2025 TPP Stakeholder meeting, available at: https://stakeholdercenter.caiso.com/InitiativeDocuments/2025-2026-TPP-SHMeeting1-DraftStudyPlan.pdf

[3] 2024 CAISO White Paper, Transmission Capability Estimates for use in the CPUC’s Resource Planning Process, August 28, 2024, available here: https://www.caiso.com/documents/transmission-capability-estimates-white-paper-2024.pdf 

[4] CAISO lists CPUC recommendations as guidance, CAISO’s draft study plan, p. 81.

3. Please provide your organization's comments on the draft Economic Assessment

Staff has no comments at this time on the draft Economic Assessment.

4. Please provide your organization's comments on the draft Frequency Response Assessment

Staff has no comments at this time on the draft Frequency Response Assessment.

5. Please provide your organization's Economic Study Requests

Staff has no comments at this time on the Economic Study Requests.

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

Staff has no comments at this time on the MIC Expansion Requests.

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

Staff has no additional comments at this time.

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Staff has no additional comments at this time.

California Public Utilities Commission - Public Advocates Office
Submitted 03/12/2025, 02:52 pm

Contact

Kanya Dorland (kanya.dorland@cpuc.ca.gov)

1. Please provide your organization's comments on the draft Reliability Assessment

The Public Advocates Office at the California Public Utilities Commission (Cal Advocates) provides these comments on the California Independent System Operator’s (CAISO) 2025-2026 Draft Transmission Study Plan and stakeholder meeting on February 26, 2025.  Cal Advocates is an independent ratepayer advocate with a mandate to obtain the lowest possible rates for utility services, consistent with reliable and safe service levels and the state’s environmental goals.[1]

 


[1] Cal. Pub. Util. Code, § 309.5.

2. Please provide your organization's comments on the draft Policy Assessment

Cal Advocates Requests CAISO Reduce the Capacity and Costs of the Conceptual Transmission Upgrades It Provides for Use in the California Public Utilities Commission’s Integrated Resource Planning Proceeding.

CAISO provides transmission capacity estimates to the California Public Utilities Commission (CPUC) for use in its Integrated Resource Planning (IRP) proceeding.[1]  These capacity estimates are used to determine whether planning portfolio resource selections would trigger transmission upgrades.  This information is necessary to determine the “least cost” resource procurement to meet the state’s clean energy targets.  In addition to providing information on the existing available transmission capacity for new resources, CAISO also provides conceptual transmission upgrades to address specific anticipated constraints, and the estimated costs of the upgrades.[2]  The conceptual upgrades provided do not appear to align with the state’s goal of least cost resource procurement because they tend to provide more capacity than is needed and at excessive costs.[3],[4]

For the 2024-2026 IRP cycle, the CPUC developed generic transmission upgrades to better fit the state’s resource needs.[5] These generic upgrades will be used in the IRP resource portfolio analysis if CAISO’s conceptual upgrades are “cost prohibitive.”[6]

Since the CPUC is developing its own generic transmission upgrades, Cal Advocates requests that CAISO revise the conceptual transmission upgrade information it provides to the CPUC to better match the state’s needs.  CAISO should provide incremental upgrades with capacity increases that are closer to the state’s needs.[7]  CAISO should also provide information on the capacity increases possible with deployment of grid enhancing technologies, including energy storage on specific constraints.  With this information, the IRP will have better information to select the least cost resource planning portfolio.  This improvement should lead to better results for California ratepayers in the IRP proceeding and the CAISO Transmission Planning Process (TPP).

 


[1] Transmission Capability Estimates for use in the CPUC’s Resource Planning Process White Paper Version 2024, August 28, 2024, CAISO at p. 3.

[2] Transmission Capability Estimates for use in the CPUC’s Resource Planning Process White Paper Version 2024, August 28, 2024, CAISO at p. 9. The cost estimates are provided in 2022 dollars.

[3] Policy-driven Assessment Unified Planning Assumptions & Study Plan, 2025-2026 Transmission Planning Process Stakeholder Meeting, (Presentation), February 26, 2025 at p. 67. For example, for the Collinsville-Tesla 500 kilovolt (kV) constraint, CAISO provide a conceptual upgrade with 8,645 megawatts (MW) of capacity for $2,852 million.  In contrast, the IRP resource portfolio for 2040 needs only a capacity increase of 600 MW on the Collinsville-Tesla 500 kV constraint.

[4] Comments of the Public Advocates Office in Response to the Administrative Law Judge’s Ruling Seeking Comments on the Busbar Mapping of Electricity Resource Portfolios For 2025-2026 Transmission Planning Process, Rulemaking 20-05-003, November 19, 2024 at pp. 1-3.

[5] Input & Assumptions 2024 – 2026 Integrated Resource Planning (IRP), February 2025, CPUC Energy Division at p. 97.

[6] Draft 2025 Inputs and Assumptions (I&A) for the 2024-2026 IRP Cycle, February 27, 2025, CPUC Energy Division, at p. 78.

[7] Draft 2025 Inputs and Assumptions (I&A) for the 2024-2026 IRP Cycle, February 27, 2025, CPUC Energy Division, at p. 105.

3. Please provide your organization's comments on the draft Economic Assessment

Cal Advocates has no comments on the draft Economic Assessment at this time.

4. Please provide your organization's comments on the draft Frequency Response Assessment

Cal Advocates has no comments on the draft Frequency Response Assessment at this time.

5. Please provide your organization's Economic Study Requests

Cal Advocates has no comments on the Economic Study Requests at this time.

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

Cal Advocates has no comments on the Maximum Import Capability (MIC) expansion requests at this time.

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

Cal Advocates has no comments on the Transmission Planning Process Infrastructure-related policy concepts at this time.

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

A. Cal Advocates Requests a Special Study on Proposed Data Center Transmission Investments in California to Confirm Investments are Least Regrets and Right-Sized.

Cal Advocates requests a special study on transmission investments proposed to support new data center growth in this TPP cycle for two reasons.  First, while it is likely that within the next 15 years, new data centers may locate within California, it is possible that a percentage of the estimated data centers may not.  Also, California’s data center vacancy rate is currently 10% in comparison to the national average which is 5%.[1]  For these reasons, the state should determine new investments to support data centers that are least regret options.

Second, data centers can reduce their load needs through the following means:

  1. Participation in Demand Response programs based on the type of data center.
  2. Co-location with new energy generation or potential connection to microgrids or existing generation.
  3. Compliance with all applicable energy efficiency upgrade requirements, including relying on the latest plant cooling technologies.

For these reasons, the state should confirm new investments to support data centers are sized to meet the capacity needed.

B. CAISO Should Provide Updates on Projects Put On-Hold in Table Format to Assist with Determining Ratepayer Impacts from Annual Transmission Plans.

Cal Advocates requests assistance with tracking changes to CAISO’s approved transmission projects that are placed on-hold after they are approved in the CAISO TPP.  Specifically, Cal Advocates requests CAISO provide a table at the end of its annual transmission plans with information on any activity on projects that are on-hold.  This table should include the original project name, scope, costs, approval date as well as include the new project name, scope, and costs if applicable and known.  This will allow stakeholders to better track the impact of projects that are put on-hold and approved in proceeding TPP cycles on the transmission access charge and ratepayers.

To illustrate the challenges with determining the potential ratepayer impacts from approved transmission plans, Cal Advocates provides the outcomes of two transmission projects that were put on-hold after approval in the TPP.

Project 1: The Midway-Andrew project was approved in the 2012-2013 TPP cycle with a cost range between $120 and $150 million.[2]  In the 2018 TPP cycle, CAISO decided to split the Midway-Andrew project into two projects named the North of Mesa upgrade and the South of Mesa upgrade.  The South of Mesa upgrade was approved in the 2018-2019 TPP cycle with an estimated cost range of $29.6 to $59.2 million.[3]   The North of Mesa upgrade project remained on-hold with an estimated cost range of $114 million to $144 million.[4]  In the 2022-2023 TPP cycle, CAISO recommended cancelling the North of Mesa upgrade project and approving the Mesa Spare Transformer project instead with an estimated cost of $12 million to $24 million.[5]

Project 2: The Wheeler Ridge Junction project was approved in the 2013-2014 TPP cycle with an estimate cost range between $90 million and $140 million.[6]  This project was put on-hold in the 2016-2017 TPP cycle, then taken off hold in the 2017-2018 cycle,[7] and then put back on-hold in the 2019-2020 cycle.[8]  In the 2022-2023 TPP cycle, the Wheeler Ridge Junction project cost was revised with a range between $259 and $517 million.[9]  The Wheeler Ridge Junction project was then approved without much discussion in the 2023-2024 TPP cycle.[10]

Maintaining a record of changes made to projects on-hold at the end of Transmission Plans would facilitate tracking project changes and their impact on ratepayers.  Currently, CAISO provides tables at the end of Transmission Plans with the expected or completed date for new and previously approved projects.  Cal Advocates recommends that a separate table with an update on on-hold projects would improve CAISO’s existing practice.

C. CAISO Should Defer to the CEC’s Energy Demand Update Forecast as the Sole Input in the 2025-2026 TPP Cycle.

At the Draft Study Plan stakeholder meeting, Pacific Gas and Electric Company (PG&E), Southern California Edison Company (SCE), and San Diego Gas & Electric Company (SDG&E) described the steps to develop their bus level forecasts for the TPP.  All three investor-owned utilities (IOU) mentioned load growth not captured in the California Energy Commission (CEC) Integrated Energy Policy Report (IEPR) load forecast. [11],[12],[13],[14]  SCE and SDG&E indicated efforts to coordinate with the CAISO to consider load interconnection assumptions that may not be represented in the CEC’s IEPR forecast.[15],[16]  

While it is important for CAISO to have visibility into utilities’ load forecasts, Cal Advocates recommends that CAISO continue to defer to the IEPR forecast as the primary load input in the TPP for the following reasons:

  • CEC rigorously considered and vetted all the same load requests possessed by the IOUs up to the point the CEC adopted its IEPR forecast on January 21, 2025.  This forecast results from an independent assessment of nearly all the same interconnection requests that the utilities considered in their current forecast.  Because the IEPR is updated annually, the IOUs will have the opportunity to include any new interconnection request information in next year’s IEPR so that the CEC can vet this information before it is used in the TPP.
  • In contrast to the CEC’s IEPR, which includes workshops and opportunities for stakeholder comments, the IOUs have not publicly shared the specific load interconnection assumptions used to derive their load forecasts.  If the IOUs provide their load forecasts solely to CAISO, their assumptions will not be transparent or properly vetted.
  • The IEPR forecast appropriately accounts for uncertainty.  It is still not well understood how an increase in large-load interconnection requests will translate to material load growth.  Specifically, load forecasts driven by data center demands have a high degree of uncertainty driven by differing assumptions about efficiency improvements, siting constraints, and the extent to which data center customers request excess capacity or request interconnections in multiple service areas.[17]  These factors underscore the need for tempered and evidence-based approaches to forecasting load growth to avoid overestimating future data center loads and risk triggering unnecessary transmission upgrades.
  • The 2022 CPUC, CEC, and CAISO Memorandum of Understanding establishes that these agencies will recognize “a single recommended forecast set and seek to use it consistently in the transmission planning and resource procurement cycles.”[18]  If CAISO supplements or supplants the CEC load forecast inputs in the TPP, it risks deviating from this agreement.

The IEPR proceeding is the ideal forum for load serving entities to reconcile potential issues with the CEC’s load forecast.  SCE states its intent to continue to collaborate with the CAISO, CEC, and CPUC “to validate and concur on the load interconnection input assumptions before conducting the necessary planning studies.”[19]  CAISO should encourage utilities to use the IEPR proceedings rather than the TPP to inform load forecast assumptions.  If CAISO supplements TPP load forecast assumptions with information from the IOUs, it should ensure that these assumptions are transparent and clearly defined.

 


[1] California Energy Commission IEPR Workshop on California Economic Outlook, February 26, 2025 at 4:55

https://www.youtube.com/watch?v=CAs9uuPqSZA Helen Kou, BloombergNEF

[2] 2018-2019 ISO Transmission Plan, March 19, 2019, CAISO at p. 142.

[3] 2018-2019 ISO Transmission Plan, March 19, 2019, CAISO at p. 476.

[4] 2018-2019 ISO Transmission Plan, March 19, 2019, CAISO at p. 144.

[5] ISO 2022-2023 Transmission Plan, May 18, 2023, CAISO at p. 58.

[6] ISO 2013-2014 Transmission Plan, July 16, 2014, CAISO at p. 291.

[7] ISO 2017-2018 Transmission Plan, March 14, 2018, CAISO at p. 150.

[8] ISO 2019-2020 Transmission Plan, March 18, 2020, CAISO at p. 118.

[9] ISO 2022-2023 Transmission Plan, May 18, 2023, CAISO at p. 57.

[10] ISO 2023-2024 Transmission Plan, May 23, 2024, CAISO at p. 159.

[11] Draft 2025-2026 Transmission Planning Process Unified Planning Assumptions And Study Plan, February 19, 2025 at p. 33.

[12] SCE Load Allocation for Local Area Studies (Presentation), February 26, 2025 at pp. 3 & 5.

[13] SDG&E Methodologies to Derive Bus Level Forecast (Presentation), February 26, 2025 at p. 2.

[14]PG&E Transmission Planning Load Forecast General Process (Presentation), February 26, 2025 at p. 5.

[15] SCE Load Allocation for Local Area Studies (Presentation), February 26, 2025 at p. 5.

[16] SDG&E Methodologies to Derive Bus Level Forecast (Presentation), February 26, 2025 at p. 2.

[17] “Forecasts for U.S. data center energy consumption in 2030 vary widely, ranging from 120 TWh to over 600 TWh by 2030…This lack of consensus highlights the uncertainty in estimating data center growth, driven by differing assumptions about efficiency improvements and sectoral expansion.” The Future of Data Center Electrical Grid Impacts. Available at https://energeia-usa.com/data-center-grid-impacts/.

[18] Memorandum of Understanding between the California Public Utilities Commission (CPUC) and the California Energy Commission (CEC) and the California Independent System Operator Regarding Transmission and Resource Planning and Implementation, December 23, 2022 at p. 2.

[19] SCE Load Allocation for Local Area Studies (Presentation), February 26, 2025 at p. 5.

California Western Grid Development, LLC
Submitted 03/12/2025, 05:01 pm

Contact

Stephen Metague (smetague1@gmail.com)

1. Please provide your organization's comments on the draft Reliability Assessment

Cal Western has not comment

2. Please provide your organization's comments on the draft Policy Assessment
  1. Expand CAISO TEAM methodology valuation – as described in detail below, Cal Western urges CAISO to use the actual LSE RA procurement cost from 2023 or 2024 as the marginal RA resource cost in its TEAM quantification of capacity benefits .  And expand TEAM valuations to include public policy issues such as California’s clean air goals, reduced reliance on Aliso Canyon, and reduced wildfire risk. .The CAISO TEAM methodology described in the CAISO Tariff allows additional attributes to be included in benefit cost valuations. The 2025-26 TPP Study Plan should commit to incorporating additional public policy benefits in the 2025-26 TPP TEAM valuations.
  2. Expand CAISO deliverability project assessments to Include the State Public Policy directives from SB 887 – SB 887 addresses the urgent State Public Policy need for new transmission that can deliver renewable energy into  transmission constrained load centers and reduce reliance on gas fired generation by 2035.andasks CAISO to take notice of the State Public Policy needs identified in SB 887 and to act proactively. The CAISO should heed this request of the California legislature and commit to assisting in meeting the objectives of SB 887.

Cal Western will elaborate on the above requests

  1. Request #1 - Update to CAISO TEAM methodology valuation – The CAISO TEAM methodology is overly conservative and needs to be expanded to include benefits of new transmission projects that are currently not considered in TEAM cost benefit calculations. The result is that TEAM undervalues the benefits of new transmission, systematically favors retention of existing gas generation and disables CAISO from doing it job to assist in meeting public policy goals.   
  2. Cal Western urges in the 2025-26 TPP CAISO TEAM valuations include air quality benefits when new transmission can bring clean energy from r preferred but remote resources.  Criteria pollutants such as Nox, Sox and PM2.5 have significant negative health impacts on local populations, including disadvantage and underserved communities.  Other RTOs quantify and apply the benefits of reduced local pollution in cost benefit calculations.

    Reduced reliance on Aliso Canyon gas storage facility is another impact that is appropriate to assess qualitatively, if not quantitatively, in TEAM valuations .  The Commission and Governor Newsom haves identified the public policy need to reduce reliance on Aliso Canyon with the goal of shutting the facility down by 2027. It is time for CAISO to incorporate a benefit in TEAM valuations if a new transmission project is able to reduce and replace local LA Basin gas generation with new clean energy from remote solar, wind or storage resources and thereby reduce the need for local gas storage

    Another policy objective of the Commission and directly stated in SB 887  is to reduce the risk of wildfires.  If a new transmission reduces that risk, as is the case with the PTEP subsea transmission solution, that benefit should be included in TEAM projects analysis.

    The CAISO 2-26-25 TPP Study Plan presentation included slide no. 96 says:

    “The ISO will consider new infrastructure-related policy concepts in the 2025-2026 Transmission Planning Process (TPP) or the next (2025-2026) Interconnection Process Enhancements (IPE) initiative. – If neither the TPP nor IPE initiatives are appropriate venues for certain policy recommendations, the ISO will consider a new stakeholder initiative”.

    Clearly improving air quality in urban areas such as the LA Basin and Fresno is a  State Policy Objective.  Reduced reliance on Aliso Canyon is also a State Policy objective.  And  reducing the risk of wildfires is a State Policy Objective.

    CAISO can address all of these infrastructure-related policy objectives within the 2025-26 TPP under the existing TEAM methodology to recognize the benefits of the new transmission infrastructure that assists in meeting these policy objectives. 

    Request #2 - Expand CAISO deliverability project assessments to Include the State Public Policy directives from SB 887. -currently CAISO narrowly defines public policy projects as new transmission that can enable power from remote generation sites to be delivered to the Bulk Electric Power System (BES)[1].  In each IRP/TPP cycle the CPUC maps a portfolio of new resources to bus bars. CAISO then finds transmission solutions that enable delivery of energy produced from the CPUC resource portfolio to the High voltage grid. The transmission projects that are approved by CAISO are called public policy deliverability projects.

    As AB 887 points out, the CAISO definition of deliverability is too narrow. Deliverability is more than finding transmission solutions to bring the new remote power generation to the Bulk Electric System. AB 887 asks for transmission solutions t be found that bring power from remote generation source all the way to customers, especially customers in transmission constrained local areas. The CAISO should plan for and approve projects that bring power to transmission constrained local areas as part of the public policy deliverability equation.

    SB 887 explicitly creates State policy goals exclusive to transmission constrained local areas.

    SB 887 added the new Section 457.57 to the Public Utilities Code paragraph directing the CPUC to:

     “(e) (4) (A) Providing resource projections that, combined with transmission capacity expansions, are expected to substantially reduce, no later than 2035, the need to rely on nonpreferred resources in local capacity areas.”

    Paragraph (a)(h)(3)  summarizes the problem SB 887 is addressing:

    “In recent years, California has seen problems in delivering renewable energy resources and zero-carbon resources to customers, including problems caused by constraints on the transmission system. First, there are generation pockets where the total potential output from renewable energy generation exceeds the capacity of the transmission system to export that energy. Second, there are load pockets where there is insufficient transmission capacity to import the renewable energy resources and zero-carbon resources that are available. Both types of constraints should be promptly fixed so that all available renewable energy resources and zero-carbon resources can be delivered to customers”.

     

    Paragraph 454.57 paragraph (a) (h) provides additional clarity where is says:

    “(h)It is the policy of the state that planning for new transmission facilities considers the following goals:

    (1) Minimizing the risk of wildfire.

    (2) Increasing systemwide reliability and cost efficiency, including through the sharing of diverse electrical generation resources within California and with other parts of the Western Interconnection.

    (3) Eliminating transmission constraints that prevent electrical generation resources from delivering to the wider grid and that prevent importing energy into load pockets.” [emphasis added]

     

    However, the California Legislature does not have direct authority over the FERC regulated CAISO. But SB 887 is clearly a call to action for the CAISO, it says:

    457. 57 (c) Recognizing that the Independent System Operator’s Federal Energy Regulatory Commission-approved tariff requires the Independent System Operator to plan and approve new transmission facilities needed to achieve the state’s goals, it is the intent of the Legislature that the Independent System Operator shall take notice of the state policies expressed in this section.

    The CAISO 2025-26 TPP Study Plan should expand the definition of public policy deliverability projects to include planning for and approving transmission projects needed to bring new clean resources all the way to customers, especially customers in transmission constrained local areas.

     


    [1] NERC defines the BES as the high voltage AC transmission system all elements of transmission rated at 100 KV or higher.

3. Please provide your organization's comments on the draft Economic Assessment

In addition to Cal Western’s economic study request, Cal Western is proposing CAISO include the following in the 2025-26 TPP Phase 1 Study Plan and in all Economic Assessments in the 2025-26 TPP:

  1. Share with Stakeholder the RA Cost and Capacity benefit assumptions that will be used in the 2025-26 TEAM Studies.  When CAISO calculates the Local Capacity Requirement (“LCR”) benefits of potential transmission solutions using the TEAM Methodology the cost CAISO assumes for both local Resource Adequacy ( RA) and System RA have a huge impact on the Benefit/Cost (‘B/C”) ratio of any transmission solutions.  CAISO local and system RA cost assumptions must be shared with Stakeholders. The System RA and Local RA capacity assumptions in the 2025-26 TPP should be expressed as $/kw/mo. and included in the Phase 1 Study Plan.
  2. Share with Stakeholder the Gas Plant utilization findings for LCR areas.  Cal Western urges CAISO to share with stakeholders the forecast gas plant usage findings from 2025-26 TPP Production Simulation studies and LCR Studies, especially gas plant usage in transmission constrained local areas for years 2035 and 2040. This information is vital to California meeting its environmental goals, including the goal to reduce reliance on retained gas plants in transmission constrained local areas by 2035 CAISO has not given this information sufficient visibility in the past. The CAISO should commit in the 2025-26 TPP Study Plan to share this information with Stakeholders and the CPUC, especially because this information was requested by the CPUC in Decision 24-02-047.[1]
  3. Review all economic study request projects, including the Cal Western Pacific Transmission Expansion Project, based on cumulative Economic, Policy, and Reliability benefits. Cal Western asks CAISO to include a commitment to assess cumulative economic, policy and reliability benefits of projects for all projects requests that are selected for detailed review.  This commitment should be stated in the final Phase 1 Study Plan for the 2025-26 TPP along with a commitment to share conclusions on the merits of each of these benefits with stakeholders in the draft 2025-26 TPP draft report.

 


[1] In CPUC Decision CPUC February 15, 2024, Decision 24-02-047, Adopting Preferred System Plan, and other matter at page 76 CPUC said:

“Conducting locational analysis within the context of IRP is difficult, because much of our analysis historically has been focused at the system level. The CAISO, however, has the ability to do much more granular and detailed analysis of local reliability needs. Therefore, we find it prudent to ask the CAISO to conduct this sensitivity analysis for the 2024-2025 TPP.”

4. Please provide your organization's comments on the draft Frequency Response Assessment

Cal Western has not comment

5. Please provide your organization's Economic Study Requests

California Western Grid Development LLC Economic Study Request in the 2025-26 TPP

March 12, 2025

California Western Grid Development LLC (“Cal Western” or ”CWG”) appreciates the opportunity to submit this economic study request for the Pacific Transmission Expansion Project (“PTE” or “PTEP”) in the 2025-2026 Transmission Planning Process (“2025-2026 TPP”).[1] We also hereby request that CAISO study the PTEP as a transmission solution to reliability needs, and State Public Policy needs, including those identified in Senate Bill No. 887 (“SB 887”). Given that PTEP addresses all these various needs, we request that the CAISO consider these study requests at the appropriate time in the 2025-2026 TPP. We also request that the PTEP be analyzed as a Multi-Value Project (“MVP”) based on its cumulative reliability, economic, deliverability, and public policy benefits, as contemplated and provided for in the Study Plan. We appreciate the CAISO clarifying the role of MVP’S in the Study Plan. Analyzing all the benefits of a project is the best approach for “no regrets” planning.

The PTEP is currently being studied in the 2024-2025 TPP as both a reliability and economic project and we also requested it be studied as an MVP project. PTEP is a controllable 2,000 MW HVDC system utilizing subsea cables, which the CAISO has previously found will allow existing power available at the Diablo Canyon 500 kV switchyard, new sources of offshore wind (“OSW”), or other new sources of renewable energy to be delivered to and between northern and southern California. CAISO has determined that a similar configuration can reduce Local Capacity Requirements (“LCR’s”) in the West LA Basin by approximately 1,993 MW, thereby displacing the need to rely on a similar amount of local capacity. An alternative project configuration with the same LCR benefit consists of a new substation at Morro Bay looped into the existing Gates to Diablo Canyon 500 kV transmission line. Cal Western requests that PTEP be studied in the 2025-2026 TPP, with the following HVDC converter stations:

  • One 2,000 MW, ±525 kV HVDC bipole converter station located at the northern terminus of the project, connecting either at the Diablo Canyon 500 kV AC station or a future Morro Bay 500 kV AC station.
  • One 2,000 MW, ±525 kV HVDC bipole converter station located at a site in El Segundo, with underground HVDC cables from the shoreline to the converter, and the following AC connections:
    • Two 220 kV AC underground cable circuits to El Nido substation; and
    • Two 220 kV AC underground and offshore cable circuits to Redondo substation.

Cal Western also encourages CAISO to evaluate different configurations of the PTEP, to the extent CAISO Staff thinks appropriate, including multi-terminal configurations and alternative points of interconnection (“POI’s”).

In the 2021-2022 TPP Report, at page 292, the CAISO stated that:

The potential PTE project benefit of reducing capacity requirements needs to be reassessed in future planning cycles as the assumptions change, particularly if the need to retain the existing gas-fired fleet for system-wide resource reliability purposes is relaxed.

Some of the important assumptions in the 2025-2026 Study Plan relevant to the study of the PTEP have changed and warrant the reassessment of the PTEP. The CAISO is also about to issue its 2024-25 TPP findings on the long-term Local Capacity Requirement (“LCR”) Study and analysis of the CPUC high gas retirement sensitivity portfolio, both of which are expected to show a need for new transmission to address local transmission constraints, including in Los Angeles.

In our comments on the 2025-26 TPP Study Plan filed today, we request CAISO to make available to Stakeholders the amount of gas plant usage found in production simulation runs used to evaluate both the base and sensitivity portfolios in the 2025-26 TPP, and especially the gas plant usage in transmission constrained local areas. This is particularly important because Senate Bill No. 887 (“SB 887”), that was unanimously approved in 2022, and signed by the Governor into law identifies an urgent State Public Policy need for new transmission that can deliver renewable energy into transmission constrained load centers and reduce reliance on gas-fired generation by 2035.  SB 887 points out that CAISO’s FERC approved tariff requires CAISO to plan and approve transmission needed to meet state, federal, and local public policy needs, and the legislature requests CAISO to take notice of the State Public Policy needs identified in SB 887 and to act proactively. Given the 10 year or more lead time for new transmission it is imperative that the CAISO plan and approve transmission now to reduce the need to rely on gas plants in local areas like LA.

As we also point out in our March 7, 2025, comments filed with the California Public Utilities Commission with respect to the appropriate inputs and assumptions for its Integrated Resource Plan (“IRP”), RA procurement from gas plant owners is seeing quickly escalating prices. The RA procurement prices paid by LSEs exceed the cost of maintaining gas plants.[2]  It seems evident that gas plant owners will also have increased market power, especially in transmission constrained local areas where a significant share of RA needs must be met by local gas plants. Gas generators’ market power and local RA prices are likely to continue to increase until new long lead time transmission allows local batteries and remote energy sources to compete to supply local RA. This information must be considered in determining whether new transmission is economic, especially in transmission constrained local areas like LA.

Clearly the need for new transmission is growing. The CPUC’s very recent February 20, 2025, Decision in R.20-05-003[3] transmits a Base Case Portfolio for the CAISO to use for transmission planning for the 20254-2026 TPP that will surely drive the need for significant new transmission. It includes the following:

  •  Over 60 gigawatts (GW) of new generation and storage resources by 2035 and nearly 100 GW by 2040. This is on top of the dramatic increases already reflected in the pre-existing resource mix
  • The adopted 2025-2026 portfolio continues to model decreased use of natural gas plants in the CAISO-system throughout the modeling time frame, with a projected 71 percent decline in annual natural gas generation in terawatt-hours by 2035 as compared to the first modeled year, 2026. By 2040, modeled natural gas usage in the adopted portfolios is reduced by 80 percent from the modeled 2026 usage[4].  A claim that CPUC has admitted it does not have local area modeling granularity to verify and has asked the CAISO assistance to use its modeling capability for transmission constrained local areas to verify. [5]
  • An increase in gross peak load of 5% by 2035 compared to 2024-25 TPP load assumptions and an increase in annual retail sales increase 6.4 TWh in 2035, or a 3% increase compared to 2024-25 TPP assumptions.[6]

In Cal Western’s October 14, 2022, filing for the 2022-2023 TPP[7], we submitted an independent analysis performed by E3 of the benefits the PTEP will provide, even if the gas plants remain in service through the study period (“E3 Analysis”). The E3 Analysis is also discussed in Cal Western’s October 2023 request to be studied in the 2023-2024 TPP. Cal Western hereby incorporates herein by reference these prior study requests and will not repeat the many benefits analyzed therein. The E3 analysis concludes that, without retirement of any gas generation and without quantifying many of the known benefits of the PTEP (wildfire risk reduction, reduced reliance on Aliso Canyon, air quality improvement especially among underserved communities), economic benefits of the PTEP would offset more than fifty percent (50%) of the PTEP’s cost. And the benefits not quantified include environmental air quality benefits that lie at the core of the State’s energy goals, as well as wildfire mitigation benefits that SB 887 requires to be considered in planning new transmission. Thus, we urge the CAISO to evaluate the benefits of the PTEP in terms of the cumulative “multi-valued” benefits the PTEP provides, including the benefit of accommodating the need for transmission to meet State Public Policy needs identified in SB 887. A silo approach to analyzing benefits is sure to ignore the true value of a project like the PTEP.[8] In terms of quantifying the benefits of the PTEP, we request that the CAISO utilize the E3 methodology, which anticipates storage (not gas-fired generation) becoming the marginal Resource Adequacy resources in the 2030’s and beyond. The E3 methodology is described in detail in the October 14th filing. To the extent necessary or appropriate we will provide an update to the E3 Analysis prior to the CAISO’s economic study.[9]

Importantly, we disagree with CAISO’s historic approach of using conservative valuations for LCR benefits as mentioned above. We believe the E3 methodology is a superior approach to calculating LCR benefits and should be used by the CAISO to quantify LCR reduction benefits.

Recent events demonstrate how significantly CAISO understates the cost of continued operation of gas plants in its LCR analysis, especially in transmission constrained local areas. The California Department of Water Resources recently contracted for resources needed to create the AB 205 California Strategic Reserve. It is an excellent example of the extraordinary prices that a fossil generator located in transmission constrained local area could demand for Local RA procured through the CPUC IRP proceeding or through the CAISO emergency procurement provisions. The capacity payments alone for the 2,859.3 MW of LA Basin strategic reserve from the Long Beach, Huntington Beach and Oxnard gas power plants ranged from $8.82/kw/mo. to $10.95 /kw/mo.[10] We now find that those prices were a bargain compared the prices recently paid for RA Procurement where the average price of RA was $11.05 /kw/mo. and RA procurement prices in many local area were an additional $5.00/kw/mo. [11]

Cal Western submits that the CAISO TPP will not achieve its objective of providing helpful information to State policy makers and regulatory agencies by continuing to use “conservatively” low or outdated values for local capacity.

We agree with and support the CAISO’s previous comment to the CPUC that transmission solutions can have long lead times and, therefore “planning for transmission-dependent projects should start as soon as possible.”[12] Indeed, if the State is to reach its 2030, 2035, and 2045 greenhouse gas (“GHG”) SB 100 requirements in a reliable and least-cost manner, the CAISO must begin planning now for transmission solutions that reduce LCRs that currently cause reliance on local fossil fuel-fired resources. To do so, CAISO will need to change its highly conservative assumptions and use realistic capacity values in its economic analysis and begin to incorporate the actual market price that is being paid for RA Procurement, a price that is currently 400%+ higher the CAISO’s conservative  cost of operating and maintaining the generation plants that has been used in previous LCR capacity studies.

We appreciate CAISO’s consideration of this request to re-study the PTEP in the 2025-26 TPP consistent with the comments herein. We are available to discuss PTEP’s many benefits with CAISO transmission planners at your convenience.

Thank you for your consideration.

Sincerely,

Marty Walicki

Martin Walicki

on behalf of California Western Grid Development, LLC

 

 

 


[1] We are simultaneously submitting comments on the 2025-2026 Draft Study Plan through the ISO’s commenting tool, using the template provided on the process webpage: • ttps://stakeholdercenter.caiso.com/RecurringStakeholderProcesses/2025-2026-Transmission-planning-process

[2] See footnote 4 below.

[3] Decision Transmitting Electricity Resource Portfolios To The California Independent System Operator For 2025 2026 Transmission Planning Process signed by the Commission at its February 20, 2025, meeting. https://docs.cpuc.ca.gov/SearchRes.aspx?docformat=ALL&docid=557879249

 

 

[4] See CPUC IRP portfolio fact sheet: https://www.cpuc.ca.gov/-/media/cpuc-website/divisions/energy-division/documents/integrated-resource-plan-and-long-term-procurement-plan-irp-ltpp/2024-2026-irp-cycle-events-and-materials/assumptions-for-the-2025-2026-tpp/2025-02-20-25_26tpp_d_factsheet.pdf

[5] CPUC Decision 24-02-047 dated February 15, 2025, page 79.

[6] See CPUC 2025-2026 Transmission Planning Process (TPP) Proposed Decision dated 1-10-25 slide 11:

https://www.cpuc.ca.gov/-/media/cpuc-website/divisions/energy-division/documents/integrated-resource-plan-and-long-term-procurement-plan-irp-ltpp/2024-2026-irp-cycle-events-and-materials/assumptions-for-the-2025-2026-tpp/25-26-tpp-pd-resolve-and-servm-analysis-slide-deck.pdf

[7] (“October 14th Filing.)” See, pp 30-32 of Attachment A.

[8] See also, October 14th Filing at 32.

[9]

[10] See Cal Matters article by Rachel Becker dated August 15, 2023, which states: “……. three power plants in Long Beach, Huntington Beach and Oxnard will be kept in reserve for three more years to feed energy into the state’s grid during power emergencies” ……” The state agreed to pay the plants’ operating companies about $1.2 billion from 2024 through the end of 2026 to stand by during energy events, such as heatwaves.” https://calmatters.org/environment/2023/08/southern-california-natural-gas-plants-remain-open/

[11] Workshop on Track 3 Revised LOLE Study and Price Mitigation Proposals 01/23/2025, see slide 36 from Appendix B to Loss of Load Expectation Study for 2026: Revised Slice of Day Tool Analysis deck. file:///C:/Users/smeta/OneDrive/Documents/CPUC%20RA%20WorkshopSlides_1-23-2025%20RA%20Prices.pdf;

See also: See CPUC paper on Local Capacity Requirement Reduction Compensation Mechanism 3/22/2024: https://www.cpuc.ca.gov/-/media/cpuc-website/divisions/energy-division/documents/resource-adequacy-homepage/resource-adequacy-compliance-materials/lcr-rcm-2024.pdf

[12] See CAISO comments filed on March 12, 2020, with respect to the Administrative Law Judge’s Proposed Decision on the “2019-2020 Electric Resource Portfolios to Inform Integrated Resource Plans and Transmission Planning”.

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

Cal Western has no comment

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
  1. Request #1 - Update to CAISO TEAM methodology valuation – The CAISO TEAM methodology is overly conservative and needs to be expanded to include benefits of new transmission projects that are currently not considered in TEAM cost benefit calculations. The result is that TEAM undervalues the benefits of new transmission, systematically favors retention of existing gas generation and disables CAISO from doing it job to assist in meeting public policy goals.  
  2. Cal Western urges in the 2025-26 TPP CAISO TEAM valuations include air quality benefits when new transmission can bring clean energy from r preferred but remote resources.  Criteria pollutants such as Nox, Sox and PM2.5 have significant negative health impacts on local populations, including disadvantage and underserved communities.  Other RTOs quantify and apply the benefits of reduced local pollution in cost benefit calculations.
  3. Reduced reliance on Aliso Canyon gas storage facility is another impact that is appropriate to assess qualitatively, if not quantitatively, in TEAM valuations .  The Commission and Governor Newsom haves identified the public policy need to reduce reliance on Aliso Canyon with the goal of shutting the facility down by 2027. It is time for CAISO to incorporate a benefit in TEAM valuations if a new transmission project is able to reduce and replace local LA Basin gas generation with new clean energy from remote solar, wind or storage resources and thereby reduce the need for local gas storage
  4. Another policy objective of the Commission and directly stated in SB 887  is to reduce the risk of wildfires.  If a new transmission reduces that risk, as is the case with the PTEP subsea transmission solution, that benefit should be included in TEAM projects analysis.

    The CAISO 2-26-25 TPP Study Plan presentation included slide no. 96 says:

    “The ISO will consider new infrastructure-related policy concepts in the 2025-2026 Transmission Planning Process (TPP) or the next (2025-2026) Interconnection Process Enhancements (IPE) initiative. – If neither the TPP nor IPE initiatives are appropriate venues for certain policy recommendations, the ISO will consider a new stakeholder initiative”.

    Clearly improving air quality in urban areas such as the LA Basin and Fresno is a  State Policy Objective.  Reduced reliance on Aliso Canyon is also a State Policy objective.  And  reducing the risk of wildfires is a State Policy Objective.

    CAISO can address all of these infrastructure-related policy objectives within the 2025-26 TPP under the existing TEAM methodology to recognize the benefits of the new transmission infrastructure that assists in meeting these policy objectives. 

    Request #2 - Expand CAISO deliverability project assessments to Include the State Public Policy directives from SB 887. -currently CAISO narrowly defines public policy projects as new transmission that can enable power from remote generation sites to be delivered to the Bulk Electric Power System (BES)[1].  In each IRP/TPP cycle the CPUC maps a portfolio of new resources to bus bars. CAISO then finds transmission solutions that enable delivery of energy produced from the CPUC resource portfolio to the High voltage grid. The transmission projects that are approved by CAISO are called public policy deliverability projects.

    As AB 887 points out, the CAISO definition of deliverability is too narrow. Deliverability is more than finding transmission solutions to bring the new remote power generation to the Bulk Electric System. AB 887 asks for transmission solutions t be found that bring power from remote generation source all the way to customers, especially customers in transmission constrained local areas. The CAISO should plan for and approve projects that bring power to transmission constrained local areas as part of the public policy deliverability equation.

    SB 887 explicitly creates State policy goals exclusive to transmission constrained local areas.

    SB 887 added the new Section 457.57 to the Public Utilities Code paragraph directing the CPUC to:

     “(e) (4) (A) Providing resource projections that, combined with transmission capacity expansions, are expected to substantially reduce, no later than 2035, the need to rely on nonpreferred resources in local capacity areas.”

    Paragraph (a)(h)(3)  summarizes the problem SB 887 is addressing:

    “In recent years, California has seen problems in delivering renewable energy resources and zero-carbon resources to customers, including problems caused by constraints on the transmission system. First, there are generation pockets where the total potential output from renewable energy generation exceeds the capacity of the transmission system to export that energy. Second, there are load pockets where there is insufficient transmission capacity to import the renewable energy resources and zero-carbon resources that are available. Both types of constraints should be promptly fixed so that all available renewable energy resources and zero-carbon resources can be delivered to customers”.

     

    Paragraph 454.57 paragraph (a) (h) provides additional clarity where is says:

    “(h)It is the policy of the state that planning for new transmission facilities considers the following goals:

    (1) Minimizing the risk of wildfire.

    (2) Increasing systemwide reliability and cost efficiency, including through the sharing of diverse electrical generation resources within California and with other parts of the Western Interconnection.

    (3) Eliminating transmission constraints that prevent electrical generation resources from delivering to the wider grid and that prevent importing energy into load pockets.” [emphasis added]

     

    However, the California Legislature does not have direct authority over the FERC regulated CAISO. But SB 887 is clearly a call to action for the CAISO, it says:

    457. 57 (c) Recognizing that the Independent System Operator’s Federal Energy Regulatory Commission-approved tariff requires the Independent System Operator to plan and approve new transmission facilities needed to achieve the state’s goals, it is the intent of the Legislature that the Independent System Operator shall take notice of the state policies expressed in this section.

    The CAISO 2025-26 TPP Study Plan should expand the definition of public policy deliverability projects to include planning for and approving transmission projects needed to bring new clean resources all the way to customers, especially customers in transmission constrained local areas.


8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Cal Western has no additional comments

Fervo Energy Company
Submitted 03/12/2025, 02:31 pm

Submitted on behalf of
Fervo Energy Company

Contact

Sarah Harper (sarah.harper@fervoenergy.com?)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

Fervo Energy Company (“Fervo”) appreciates the opportunity to provide input on the CAISO 2025-2026 Transmission Planning Process (“TPP”) Draft Study Plan. Fervo requests that CAISO consider the tremendous geothermal resources being developed in Nevada and Utah for import into the CAISO. Robust transmission planning analysis in advance of this influx of geothermal energy will be critical to deliver clean, firm, reliable power into the CAISO to meet reliability requirements and clean energy mandates.

  1. CAISO should include geothermal in the assessment of transmission needed to support out-of-state resources in the 2025-26 TPP cycle.

CAISO’s 2023-24 20-Year Transmission Outlook acknowledges that geothermal resources and out-of-state resources, among others, are expected to play a greater role in achieving California’s reliability and climate goals and that these resources create unique challenges in the planning and interconnection processes.[1] The resource portfolio approved for the 2025-26 TPP cycle begins to reflect the growth in geothermal capacity from Utah and Nevada, mapping over 900 GW to these areas by 2035. Additionally, the draft Inputs & Assumptions being developed by the CPUC for the 2024-2026 IRP cycle reflect the likelihood of even more growth by adding Enhanced Geothermal Systems (EGS) as a candidate resource, significantly increasing geothermal potential for future portfolios.[2]

Several notable technological advances applied over the last five years have majorly expanded geothermal energy power production potential across the west. Namely, bench development and horizontal drilling advancements honed during the shale revolution have unlocked the ability to access additional layers of geothermal resource per well pad, resulting in a higher density of power generation per acre than hydrothermal approaches have been previously capable of.

Moreover, accessing more geothermal resources per well pad facilitates more total available resources at a project as it lowers project costs, allowing the most cost effective and optimized deployment of capital. The resource potential estimates previously considered in state planning efforts have sited outdated analysis based on the spacing of vertical wells without horizontal drilling applications or bench development concepts. Not only does this technology application improve our resource efficiency and power density but also allows EGS to produce two to five times the amount of power from the same footprint as a single bench design.[3] 

Despite this expected increase in geothermal resources’ contribution to resource portfolios, CAISO’s 2025-26 TPP study plan makes no mention of the necessity to begin adapting the planning process to prepare for it. In anticipation of increased geothermal growth in future cycles, Fervo recommends that CAISO include geothermal in this year’s assessment of transmission needed to support out-of-state resources.

  1. CAISO should begin analysis for OOS geothermal in the 2025-2026 TPP cycle.

The Draft Study Plan states that CAISO will carefully analyze the needs for out-of-state (OOS) wind on new out-of-CAISO transmission.[4] The CPUC recommended this analysis to accommodate the significant increase in OOS wind in this year’s resource portfolio compared to prior years.[5] Due to the complexity of this analysis, CAISO is taking an extra year to determine the most efficient transmission solutions for these resources and to better understand the options, costs, and potential collaborations with other Balancing Area Authorities.[6] In other words, given the complexity of developing new transmission for OOS resources, CAISO needs two years instead of one to develop potential mitigation strategies.

Fervo agrees that the process of developing transmission for OOS resources is complex and may require extra time and attention. Fervo encourages CAISO to begin this analysis for OOS geothermal in the 2025-26 cycle. Although the expected OOS geothermal growth has not yet fully materialized in the CPUC’s 2025-26 TPP portfolio, it is clearly indicated by both CAISO’s 20-Year Transmission Outlook and the CPUC’s proposed 2024-26 IRP cycle assumptions. Rather than waiting for future CPUC resource plans to reflect this growth and then having to delay the necessary transmission by a year as was required for OOS wind in this cycle, CAISO should begin the assessment of transmission needs for future OOS geothermal now to better align with anticipated geothermal growth.

Fervo appreciates the opportunity to submit these comments in response to the CAISO 2025-2026 TPP Draft Study Plan.  

 


[1] 2025-2026 Transmission Planning Process Unified Planning Assumptions and Study Plan DRAFT dated February 19, 2025, p. 9.

[2] 2025_draft_inputs_and_assumptions_doc_20250220.pdf, p. 9.

[3]  Fervo Energy Technology Day Presentation. 2024. https://fervoenergy.com/technology/ 

[4]  2025-2026 Transmission Planning Process Unified Planning Assumptions and Study Plan DRAFT dated February 19, 2025, p. 82.

 

[5]  Decision Transmission Resource Portfolios for the 2025-26 TPP, pp. 61-62

[6] 2025_draft_inputs_and_assumptions_doc_20250220.pdf, p. 82.

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Golden State Clean Energy
Submitted 03/12/2025, 05:02 pm

Contact

Ian Kearney (ian@goldenstatecleanenergy.com)

1. Please provide your organization's comments on the draft Reliability Assessment

No comment

2. Please provide your organization's comments on the draft Policy Assessment

No comment

3. Please provide your organization's comments on the draft Economic Assessment

No comment

4. Please provide your organization's comments on the draft Frequency Response Assessment

No comment

5. Please provide your organization's Economic Study Requests

Golden State Clean Energy (“GSCE”) submits the Monarch 500 kV Transmission Project (“Monarch” or “the Project”) as an Economic Planning Study Request that provides a cost-effective upgrade to the Path 15 corridor. The Project may involve participation from non-CAISO Balancing Authority members, which can help reduce CAISO customer costs while providing broad benefits for the CAISO system. Monarch is currently being studied by the Western Area Power Administration (“WAPA”) Sierra Nevada Region (“SNR”) in relation to solar and storage projects in the WAPA SNR queue.[1]  GSCE understands that CAISO is aware of the Project from an affected system perspective, but the Project and the corresponding solar and storage in the WAPA SNR queue could benefit LSEs in CAISO’s footprint if CAISO were to study the transmission Project so the transmission capacity is shared between CAISO and the Balancing Authority of Northern California. GSCE is also currently engaged in discussions with an LSE in CAISO’s footprint regarding generation from the Project, and thus there is existing commercial interest in Monarch within the CAISO BAA.

 

GSCE appreciates CAISO including the Monarch as an Economic Planning Study Request in the 2024-2025 transmission planning process. GSCE resubmits the Project in this TPP cycle given the 2024-2025 transmission planning process is still ongoing and Monarch continues to provide economic benefits as well as support for CAISO policy and reliability needs.[2]

 

GSCE urges CAISO to consider Monarch as one of the priority economic requests to be studied because the Monarch Project has the potential to mitigate Path 15 corridor congestion, which is a major contributor to congestion identified in the 2024-2025 TPP cycle. The Monarch Project would pair well with a Manning-Moss Landing 500 kV upgrade if Monarch is connected to the CAISO system as part of a broader regional upgrade. The Path 15 corridor and the Moss Landing-Las Aguilas 230 kV line provide important transmission pathways for cost-effective Fresno area solar and storage to serve load in the Bay Area. However, these two corridors showed a very large increase in the cost of congestion in the preliminary study results in 2024-25 TPP. CAISO’s preliminary base case analysis found that congestion on the Path 15 corridor and the Las Aguilas-Moss Landing 230 kV Line are the two most costly branch groups studied in both 2034 and 2039.[3]

 

GSCE supports 500 kV upgrade solutions to the significant and costly congestion observed in CAISO’s preliminary economic analysis of the Path 15 corridor and the Moss Landing-Las Aguilas 230 kV Line. In addition, the 20-Year Transmission Outlook (2024) identified 500 kV upgrades to these two pathways as likely needed in the long-term.[4]  CAISO suggested in the 2023-2024 Transmission Plan that upgrades to the Path 15 corridor and the Moss Landing-Las Aguilas 230 kV Line likely should be planned in tandem, stating that “mitigations for one constraint may impact the flow and even aggravate the congestion on the other constraints because of the topology connection between these two constraints.”[5]

 

GSCE believes that Monarch, in combination with a Manning-Moss Landing 500 kV Line, provides a cost-effective, long-term solution to the region that meets both policy, economic, and reliability needs.

 


[1] The Monarch 500 kV Transmission Project is the transmission project associated with the Fresno County solar plus storage projects in the WAPA SNR queue. See WAPA SNR queue number 2023-G1 and 2023-G2.

[2] For more information on the multi-benefits Monarch can provide, see GSCE’s comment on the November 2024 stakeholder meeting in the 2024-2025 TPP discussing preliminary policy and economic study results.

[3] CAISO 2024-2025 TPP, Policy & Economic Preliminary Assessment and Study Updates (presentation), slides 26-30, 43-45, Nov. 13, 2024.

[4] CAISO, 20-Year Transmission Outlook, pg. 67, July 31, 2024. The 20-Year Transmission Outlook identified overloads on the Los Banos-Tracy 500 kV line and underlying 230 kV system that could be mitigated by a new Manning-Tracy 500 kV line, as well as an overload on the Manning-Los Banos 500 kV line and the 230 kV path from Panoche to Moss Landing (which includes the Moss Landing-Las Aguilas 230 kV line) that could be addressed by a Manning-Moss Landing 500 kV line that would also provide another 500 kV line to the Bay Area. Id.

[5] CAISO, 2023-2024 Transmission Plan, Appendix G, pg. G-49, May 23, 2024.

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

No comment

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

No comment

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

No comment

Grid United LLC
Submitted 03/12/2025, 11:57 am

Contact

Gimod Mathew (gimod.mathew@gridunited.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests

Kern-Southland Energy Link LLC is pleased to submit the Kern-Southland Energy Link (K-SEL) project to the CAISO for consideration as an economic & policy study request in the 2025-2026 Transmission Planning Process. K-SEL intends on repurposing an existing underground Oil & Gas industry pipeline as the conduit for the below grade HVDC transmission cable and right-of-way. K-SEL is a multi-value project with reliability, policy, and economic benefits, and enables the deliverability of cheaper FCDS resources deep into the LA Basin. The project would provide a path from Midway 500 kV in Kern County deep into the LA Basin in the form of a controllable DC tie that could be optimized to alleviate congestion on Path 26, which experienced nearly 3,500 hours of congestion and a total cost of congestion of ~$72M in the CAISO 23-24 TPP economic assessment. We respectfully request CAISO to study K-SEL for its ability to reduce LCR and reliance on Aliso Canyon storage by providing deliverability of 2 GW of cheaper resources into the LA Basin without major upgrades to the intra-basin transmission system, the ability to provide voltage support to the coastal LA Basin system, and economic congestion management benefits from having a controllable North South backbone DC transmission link. The modeling and project details remain unchanged from prior submittals

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

GridLiance West (GLW)
Submitted 03/12/2025, 03:07 pm

Submitted on behalf of
GridLiance West (GLW)

Contact

Jaime Hoffman (jaime.hoffman@nexteraenergy.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests

GridLiance West (GLW) respectfully requests that the CAISO conduct economic studies in the 2025 – 2026 Transmission Planning Process on the following 3 projects (see attached):

  • Fort Churchill-Tesla
  • Sloan Canyon-Mead and Mead-Crystal-Navajo-Shiprock-Four Corners 
  • Western Bounty-GLW Esmeralda Interconnection
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Horizon West Transmission (HWT)
Submitted 03/11/2025, 11:37 am

Submitted on behalf of
Horizon West Transmission (HWT)

Contact

Jaime Hoffman (jaime.hoffman@nexteraenergy.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

Horizon West Transmission (HWT) respectfully requests that the CAISO conduct economic studies in the 2025 – 2026 Transmission Planning Process on the following 3 projects (see attached):

  • Captain Jack- Fern Road
  • Cielo Azul-Imperial Valley
  • Midway-Pastoria-Whirlwind
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

LSA
Submitted 03/12/2025, 03:52 pm

Submitted on behalf of
Large-scale Solar Association

Contact

Hillary M Hebert (hillary@hmhenergy.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

The Draft Study Plan indicates that the CPUC’s latest base case portfolios contain a greater volume of long lead-time (“LLT”) resources, such as geothermal, long-duration energy storage, and offshore wind, for the 2025-26 Transmission Planning Process (“TPP”).[1]  Given this increase, it is important for CAISO to improve the transparency of this process.  LSA appreciates CAISO’s efforts in the Interconnection Process Enhancements initiative to begin to provide details regarding deliverability reservations from previous TPP cycles.[2]  LSA suggests that CAISO should provide the following details regarding future deliverability reservations during the 2025-26 TPP cycle and beyond.

  1. Technology type
    1. e.g. offshore wind, geothermal
  2. Point of Interconnection (“POI”)
    1. e.g. Palo Verdo, Eldorado
    2. General location, like “Central Cost” offshore wind, is not sufficient because it does not indicate which substations will be impacted.
  3. The number of MWs and modeling year
    1. e.g. 1000 by 2035; 2000 additional MW by 2040
  4. The transmission upgrades, or portions of transmission upgrades that CAISO approved to support the LLT resources at the specified POI
    1. For example, if the CPUC’s resource plan indicates the need for deliverability reservations at Eldorado for 1000 MW by 2035 and an additional 2000 MW by 2040, CAISO should indicate which transmission upgrades have been approved or are being proposed to support these amounts.
    2. The data provided should include the in-service date and the total amount of deliverability created by the relevant transmission upgrade and the portion that CAISO will reserve for LLT resources.
  5. The year of the TPD cycle that the deliverability reservation will begin
    1. For example, if CAISO intends to reserve 1000 MWs of a 5000 MW transmission upgrade with an in-service date in 2035, which TPD cycle will include the deliverability that it will reserve for LLT resources?
    2. The details of how the deliverability allocation process will work, and whether LLT resources can delay their attempt to receive an allocation, will likely be considered in a future Interconnection Process Enhancements initiative, but LSA encourages CAISO to at least confirm which annual TPD cycle will include allocations of reserved deliverability for each specific upgrade.

Providing this information will enhance the integrity of the deliverability reservation process. This data is particularly critical for projects that submit interconnection applications in Merchant Zones because their ability to assess whether deliverability will be available at their Point of Interconnection could have significant financial impacts.  CAISO’s goal is to expand incremental transmission capacity to support LLT resources mapped in the CPUC’s portfolio while preserving existing transmission capacity allocated earlier in the interconnection queue.[3] Although LSA continues to question whether deliverability reservations are necessary, this additional information will help to ensure that the process is fair and transparent.

 


[1] 2025-2026 Transmission Planning Process Unified Planning Assumptions and Study Plan DRAFT dated February 19, 2025, p. 73.

[2] 2023 Interconnection Process Enhancements Track 3 Updated Final Proposal dated March 3, 2025, p. 45.

[3] 2025-2026 Transmission Planning Process Unified Planning Assumptions and Study Plan DRAFT dated February 19, 2025, p. 83.

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Mari Rose Taruc (California Environmental Justice Alliance) Heena Singh (California Environmental Justice Alliance) Katie Ramsey (Sierra Club) Julia Dowell (Sierra Club) Shana Lazerow (Communities for a Better Environment) Roselyn Tovar (Communities for a Better Environment) Lucia Marquez (Central Coast Alliance United for a Sustainable Economy) Marven Norman (Center for Community Action and Environmental Justice)
Submitted 03/12/2025, 12:20 pm

Submitted on behalf of
California Environmental Justice Alliance, Sierra Club, Communities for a Better Environment, Central Coast Alliance United for a Sustainable Economy, Center for Community Action and Environmental Justice

Contact

Heena Singh (heena@ceja.org)

1. Please provide your organization's comments on the draft Reliability Assessment

See attached for full response with footnotes. 

Section 2.1. The Regenerate California Campaign supports the 15-year planning horizon included in the 2025-2026 Draft Study Plan, with 2035 and 2040 selected as the longer-term study years. Moving from the 12-year planning horizon used in previous studies to a 15-year planning horizon is a positive step forward as it helps keep pace with the long lead times and delays in transmission development that come with achieving the state’s decarbonization goals, including opportunities for gas plant decommissioning in the future. 

 

Section 2.6 The CAISO 2025-2026 Draft Study Plan includes projects that focus on the integration of renewable energy sources and energy storage solutions. The Regenerate California Campaign recognizes these are important steps toward decreasing the state’s reliance on gas plants.

  • Energy Storage: Extensive deployment of Li-ion Battery storage systems, both 4-hour and 8-hour variants, are planned to support grid reliability and renewable integration. Long-duration energy storage (LDES) technologies like Flow Batteries and Compressed Air Energy Storage are also being considered.

    • The Regenerate Campaign supports a substantial and coordinated increase in battery storage, co-located in localities reliant on gas peaker plants and by large solar production (to mitigate dramatic evening peaking), is needed to support gas plant retirement in the future.

    • It is also necessary to expand the list of LDES resources under consideration. The current LDES definition in Appendix B of the 2025-2026 Draft Study Plan includes Flow Batteries (8-hour) and Compressed Air Energy Storage (24-hour). However, emerging technologies such as iron-air batteries (100-hour) should also be included. Iron-air batteries are a market-ready solution, with a project currently under development in PG&E’s Mendocino territory. Including such technologies would enhance the diversity and resilience of California’s energy storage portfolio, supporting the state’s transition away from gas peaker plants and furthering renewable energy integration. 

  • Retirement of Gas Capacity: The study indicates a planned reduction in gas capacity, especially in Southern California areas like Riverside and Vernon, where older gas plants are scheduled for retirement. 

    • The Regenerate California Campaign commends the planned reduction of gas capacity and appreciates CAISO’s ongoing efforts to identify these situations in advance to ensure on-time retirement. 

    • We ask that CAISO ensure the three Once Through Cooling (OTC) plants that were extended to 2026 are retired on time. 

  • Hybrid Systems and Advanced Technologies: The draft plan explores hybrid renewable systems and combining solar PV with battery storage as potential future alternatives to gas-based power generation. We further caution that while green hydrogen from renewable resources has potential as a clean energy source, it should be produced using electrolysis powered by renewable energy, carefully regulated, and prioritized only for specific use cases. 

    • See comments included in the Energy Storage bullet above. 

  • Section 2.6.5. The list of existing generators that have been identified as retiring does not appear to include details on why specific units are listed as “Denied.” We are familiar with Section 12 of the Business Practice Manual for Generator Management that includes rationale for CAISO to deny a generator’s request for plant retirement due to reliability concerns, resource adequacy or regulatory requirements. This level of detail would be helpful to include in the Retirement Table. 

These are the plants are listed on the mothballed spreadsheet but that were denied the ability to retire; they should be considered at risk of retirement in the future:

  • ??Feather River Energy Center, Unit #1

  • Metcalf Energy Center

  • Yuba City Energy Center (Calpine)

  • GREENLEAF II COGEN

  • Channel Islands Power

  • E.F. OXNARD INCORPORATED

  • Midway Sunset Cogeneration Company

  • Kingsburg Cogen 

  • Agnews Power Plant

These are plants located in or near EJ communities that will not be retired but communities have repeatedly requested analysis for retirement potential:

  • Wellhead Power Delano

  • HARBOR COGEN COMBINED CYCLE

  • McGrath Beach Peaker

  • Walnut Creek Energy Park Unit 1

  • Walnut Creek Energy Park Unit 2

  • Walnut Creek Energy Park Unit 3

  • Walnut Creek Energy Park Unit 4

  • Walnut Creek Energy Park Unit 5

  • LOS ESTEROS ENERGY FACILITY AGGREGATE

  • Russell City Energy Center

  • DELTA ENERGY CENTER AGGREGATE

  • GILROY ENERGY CENTER UNITS 1&2 AGGREGATE

  • GILROY ENERGY CENTER, UNIT #3

  • Cuyamaca Peak Energy Plant

  • El Cajon Energy Center

2. Please provide your organization's comments on the draft Policy Assessment

See attached for full response with intro and footnotes.

(Section 3.3): The 2025-2026 transmission planning portfolios have no gas plant retirements in the model years beyond the assumed retirements included in the 2024-2025 TPP modeling baseline retirements. CEJA and Sierra Club have raised concerns in comments to the CPUC that the agency has not updated its analysis or process to ensure compliance with SB 887 requirements, Section 454.57(e)(4) of the Public Utilities Code. We would request that CAISO be more explicit in how its analysis and processes are in compliance with 887; a statement without justification is insufficient. In D. 25-02-026, the CPUC acknowledged CEJA and Sierra Club concerns that further work is needed on gas retirements, especially in disadvantaged communities. While the Commission found that it is premature to consider additional gas plant retirements in this year’s base case portfolio because the CAISO 2024-2025 analysis is not complete, the Commission also stated that the results from that study should help CAISO and the CPUC plan transmission solutions for additional gas plant retirements in the future, including in local areas.  

The Regenerate California Campaign understands the rationale for waiting for CAISO to analyze the 2024-2025 base case portfolio, but there should be language in the Draft Study Plan indicating next steps/direction for the next sensitivity analysis. Despite direction from CPUC and the Draft Study, gas plants in California face significant pressure to retire, and the CAISO should be planning for the possibility that gas plants retire as a sensitivity.

(Section 3.3) The Regenerate California Campaign supports the adoption of a base case portfolio and a sensitivity portfolio with a greater volume of long lead-time (LLT) resources, mainly geothermal, long-duration energy storage (LDES) and offshore wind (OSW). These LLT resources help reduce GHG and local harms in the EJ communities around those gas-fired power plants. 

(Section 3.3) Baseline retirements are all the gas once-through cooling (OTC) plants (~3.7 GW) and assumed linear phaseout of in front of the meter combined heat and power plants (CHP) from 2031-2040, with all 1,964 MW CHPs assumed retired by 2040. The Regenerate California Campaign supports CPUC staff’s recommendation that assumes the same CHP plants identified for the 2024-2025 TPP 10-year portfolios are also retired in the 2025-2026 TPP 10-year portfolio and the full CHP list is retired for the 2040 portfolios. 

3. Please provide your organization's comments on the draft Economic Assessment

See attached for full response with intro and footnotes.

It is imperative that both the policy-driven and the economic-driven projects analyses study impacts of the proposed transmission projects on operations at existing gas-fired power plants.

4. Please provide your organization's comments on the draft Frequency Response Assessment

 The Regenerate California Campaign has no comments at this time. 

5. Please provide your organization's Economic Study Requests

 The Regenerate California Campaign has no comments at this time. 

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

See attached for full response with intro and footnotes.

The Regenerate California Campaign supports maximum import capacity (MIC) Expansion Requests that result in the firm delivery of renewable, clean, non-combustion power sources into load pockets that continue to rely on fossil fuel resources to meet local capacity requirements. The Regenerate California Campaign requests modeling to show how the MIC Expansion Requests would impact gas-fired power plant operations in EJ communities. 

 

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

The Regenerate California Campaign has no comments at this time. 

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

See attached for full response with intro and footnotes.

The California Environmental Justice Alliance (CEJA), Sierra Club, Communities for a Better Environment (CBE), Central Coast Alliance United for a Sustainable Economy (CAUSE), and Center for Community Action and Environmental Justice (CCAEJ), together as the Regenerate California Campaign, appreciate the opportunity to submit these comments on the CAISO 2025-2026 Transmission planning process. Collectively, we lead the Regenerate California Campaign, where we share a vision for California’s most impacted communities to have access to clean energy, good jobs, and clean air. Aligned with the clean energy goals and gas plan retirement outlined in key California policies, including Senate Bill (SB) 100, SB 887, and SB 350, we envision a future where all California gas plants are retired by 2035, prioritizing retiring those impacting environmental justice communities by 2030.

Gas-fired power plants are retained due to grid limitations caused by decades of underinvestment in transmission and clean new energy sources targeted to Environmental Justice (EJ) communities, including disadvantaged communities (DACs). Grid constraints are also a barrier to beneficial load growth and the interconnection and operation of local clean energy resources including battery storage located in EJ communities. This underinvestment in the electric grid impairs air quality especially in EJ areas due to the continued use of polluting sources of electric generation, delays electrifying transportation which results in continued dependence on fossil fuels for transportation and increases the frequency and duration of outages during extreme weather events.

The Regenerate California Campaign is focused on transmission and clean energy projects that enable retirement of gas-fired power plants in areas like the San Joaquin Valley and the Los Angeles Basin. Additional grid investments must be paired with efforts by transmission owners and clean energy developers to engage impacted local communities and to promote local and regional clean energy development.

The following are our high level recommendations and goals in engaging in this TPP:

  • Prioritize retiring gas plants in DACs by 2030, with a statewide goal of full retirement by 2035.

  • Include detailed rationale for denied gas plant retirements and expand visual representations of project locations in sensitivity portfolios

  • Support CAISO’s 15-year planning horizon and advocate for sensitivity analyses to plan for accelerated gas plant retirements, particularly in EJ communities.

  • Request detailed analysis and planning for the retirement of specific gas plants located in or near EJ communities, including: Wellhead Power Delano, Harbor Cogen, McGrath Beach Peaker, Walnut Creek Energy Park Units 1-5, Russell City Energy Center, Delta Energy Center, Gilroy Energy Center Units 1-3, and others listed in the letter.

The Regenerate California Campaign appreciates the graphics that the CAISO used in its earlier presentation that showed the relative location of projects included in the 2024-2025 base case portfolio for 2034 and 2039. We request that the CAISO expand this to also show the locations of projects included in the 2035 and 2040 sensitivity portfolios. 

Thank you for considering these comments. We look forward to working with you on these issues. 

Middle River Power, LLC
Submitted 03/12/2025, 07:30 pm

Contact

Brian Theaker (btheaker@mrpgenco.com)

1. Please provide your organization's comments on the draft Reliability Assessment

MRP has no comment.

2. Please provide your organization's comments on the draft Policy Assessment

MRP has no comment.

3. Please provide your organization's comments on the draft Economic Assessment

MRP has no comment.

4. Please provide your organization's comments on the draft Frequency Response Assessment

MRP has no comment.

5. Please provide your organization's Economic Study Requests

MRP has no comment.

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

MRP has no comment.

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

At the February 26, 2025 TPP meeting, the CAISO noted that it will consider “infrastructure-related policy concepts” in the 2025-2026 Transmission Planning Process (TPP) or the next (2025-2026) Interconnection Process Enhancements (IPE) initiative.  (2/26 TPP presentation deck at page 96). 

MRP has an infrastructure policy issue that it requests the CAISO consider and resolve promptly.  The issue arises from MRP’s experience at sites where MRP is co-locating a battery energy storage system (“BESS”) with an existing gas turbine.  These projects provide significant value and flexibility because the grid-charged BESS displaces much of the operation of the gas turbine, resulting in significant GHG and other emission reductions, but the gas turbine remains available to provide longer duration service as needed.  Several load-serving entities have already signed long-term contracts for these projects.

The infrastructure policy issue that requires prompt resolution is this: Due to current market modeling constraints, the market cannot recognize that the BESS and the gas turbvine cannot operate simultaneously. As a result, the CAISO could instruct the units to operate simultaneously, which amounts to an infeasible dispatch.  

The CAISO has already approved several of these projects, and they are rapidly nearing commercial operation.  MRP expects to address these market model constraints through a sub-optimal workaround.  MRP greatly appreciates that the CAISO is allowing these projects to go into commercial operation, but the sub-optimal conditions under which the projects must operate greatly reduces their value to the grid at large.

MRP requests that the CAISO address these market model constraints in its market software.  While MRP views these constraints more as implementation issues than policy issues, MRP appreciates the opportunity to submit this issue to the CAISO in this forum.  Given the appeal of these projects to off-takers to date, MRP expects that this model will gain popularity with other developers and the number of these projects will continue to increase.   

The CAISO also noted that if neither the TPP nor IPE initiatives are appropriate venues for certain policy recommendations, the ISO will consider a new stakeholder initiative.  (TPP presentation at page 96.)  MRP respectfully urges the CAISO to consider using such a new initiative, limited in scope, to address this issue, as this issue is both bounded and urgent.  The CAISO previously has used accelerated initiatives to promptly address issues with a narrow scope. 

Given that these CAISO-approved projects are nearing commercial operation, MRP requests the CAISO consider and resolve this issue as soon as possible.

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

MRP has no comment.  

Pacific Gas & Electric
Submitted 03/12/2025, 03:56 pm

Contact

Stacy Fuhrer - PG&E (stacy.fuhrer@pge.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment

To Pacific Gas and Electric Company’s (PG&E) knowledge, the last time the California Independent System Operator (CAISO) hosted a workshop providing an overview of the Transmission Economic Assessment Methodology (TEAM) method was in 2017.1 Given the increases in approved transmission projects, congestion, and resource siting trends, PG&E proposes that CAISO provide the stakeholder community with some training on the TEAM method so that stakeholders are better informed to comment about the results.  

For example, aligned with the assumption in the Integrated Resource Plan (IRP), new solar development will use the Production Tax Credit (PTC). Given the value of the PTC and the increase in the value of the Portfolio Content Category 1 (PCC1) Renewable Energy Credit (REC), PG&E is not sure that the assumption that renewables will curtail at $-25 will always be reasonable. PG&E would like to better understand the forum to discuss important assumptions like this one regarding modeled congestion prices. PG&E would also be interested in a scenario where a lower curtailment value is used (i.e., further negative).  In another example, revenues for certain resources (“owned facilities”) are assigned to load-serving entities (LSEs). PG&E understands that the CAISO is considering renewables and utility-owned generation as Owned Facilities but would appreciate further clarity.   

Please See: https://www.caiso.com/documents/agenda_presentation_transmissioneconomicassessmentmethodologydocumentationupdate.pdf 

4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Pattern Energy
Submitted 03/12/2025, 12:20 pm

Contact

Cameron Yourkowski (cameron.yourkowski@patternenergy.com)

1. Please provide your organization's comments on the draft Reliability Assessment

No comments at this time. 

2. Please provide your organization's comments on the draft Policy Assessment

Pattern Energy appreciates the Draft Study Plan’s consideration of out-of-state resources and specifically the continued focus on New Mexico wind.  Viewed together, CPUC 24-25 and 25-26 portfolio modeling results demonstrate the significant value of incremental megawatts of new New Mexico wind above what is currently under contract and construction at SunZia. 

The 25-26 portfolio identified 3,099 MW of FCDS MWs of New Mexico wind mapped to Palo Verde 500kV (intended to be delivered via the SunZia Transmission system and associated AZ Transmission Rights, including any required supplemental Transmission Rights) and also 1,750 NW of New Mexico wind mapped to Lugo 500kV (to be delivered on new-build transmission).

Pattern Energy agrees with the CPUC’s recommendation that CAISO “conduct additional analysis on potential transmission solutions and alternatives, as well as potential co-benefits for other balancing areas” (p.129, CPUC Modeling Assumptions for 2025-26 TPP).  In doing so, Pattern Energy encourages the CAISO to engage with transmission customers and transmission developers in Arizona and New Mexico to survey the potential for available existing or in-development transmission that should be appropriately assumed in this study plan.  In addition to Lugo, Willow Beach and all other potential delivery points with CA should be considered in this additional analysis to ensure the most timely and cost-effective solutions are identified.

If CAISO does identify options to increase transmission delivery between New Mexico and the CAISO interties, including all of the New Mexico wind in the 25-26 TPP, regardless of where it has been mapped, is important to ensure accurately sized deliverability upgrades within CA are identified.  This is because the Deliverability Assessment Methodology will utilize a “maximum dependable dispatch” figure that is less than the installed MW figures identified by the CPUC and better reflects the amount of associated transmission through Arizona to make those installed MWs deliverable.  Accordingly, Pattern Energy recommends that CAISO model the maximum FCDS MWs of all of the New Mexico Wind identified by the CPUC which would feasibly use any of these delivery paths.

3. Please provide your organization's comments on the draft Economic Assessment

No comments at this time. 

4. Please provide your organization's comments on the draft Frequency Response Assessment

No comments at this time. 

5. Please provide your organization's Economic Study Requests

No comments at this time. 

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

No comments at this time. 

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts

No comments at this time. 

8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Pattern supports the reservation of deliverability for New Mexico wind already identified in previous portfolios and utilizing transmission under development as such reservations are critical for enabling contracted resource under construction today.

SB Energy
Submitted 02/27/2025, 06:09 am

Contact

Aftab Alam (aftab@sbenergy.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests

CAISO is requested to include the following for Economic Study Requests:

1. Solutions to mitigate the Devers 500/230kV bank congestion such as:

a. Expansion of CRAS to include monitoring of overload on the Devers 500/230kV Transformers for various contingencies (such as loss of Devers 500/230kV Transformer #1, Devers 500/230kV Transformer #2, Loss of Serrano - Valley 500kV line or Loss of N.Gila - Imperial Valley 500kV Line) that can overload

b. Addition of a third 500/230kV Transformer at Devers.

 

2. Reconductor or Add a second Moss Landing - Las Aguilas 230kV line

 

3. Solutions to mitigate Path 15 corridor congestion

Upgrade Los Banos - Gates 500kV or Los Banos - Midway 500kV lines (Inclding lines being looped into Manning)

Upgrade Gates - Midway 500kV lines

Upgrade Panoche - Gates 230kV lines

6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com
7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting

Shell Energy North America (US), L.P.
Submitted 03/07/2025, 10:59 am

Contact

Christa Lim (christa.lim@shell.com)

1. Please provide your organization's comments on the draft Reliability Assessment
2. Please provide your organization's comments on the draft Policy Assessment
3. Please provide your organization's comments on the draft Economic Assessment
4. Please provide your organization's comments on the draft Frequency Response Assessment
5. Please provide your organization's Economic Study Requests
6. Please provide your organization's Maximum Import Capability (MIC) expansion requests. Any confidential details should not be included in this comment template and should instead be emailed to regionaltransmission@caiso.com

See attached 

7. Please provide your organizations comments on the Transmission Planning Process Infrastructure-related policy concepts
8. Please provide any additional comments on the Draft Study Plan and February 26th, 2025 Stakeholder Meeting