1.
Please provide a summary of your organization’s comments on the Eldorado 230kV Short Circuit Duty Mitigation Project.
The Public Advocates Office at the California Public Utilities Commission (Cal Advocates) is the state-appointed independent consumer advocate at the California Public Utilities Commission (CPUC). Our goal is to ensure that all Californians have affordable, safe, and reliable utility services while advancing the state’s environmental goals. Our advocacy efforts to protect California customers span the areas of energy, water, and communications regulation.[1]
Cal Advocates appreciates the opportunity to participate in the discussion on improvement options for 500 kilovolt (kV) Eldorado Substation (Eldorado Substation). Cal Advocates recognizes that the capacity at the Eldorado Substation, which is the entry point for out-of-state (OOS) resources, including wind, is critical for meeting the State’s clean energy goals. For this reason, the proposed mitigation plan is an opportunity to address both the short- and long-term needs at the Eldorado Substation to achieve the most cost-effective solution.
Project Background
Southern California Edison (SCE) determined during the 2022-2023 Transmission Planning Process (TPP) that the ratings at the 230 kV and 500 kV buses located at the Eldorado Substation would be exceeded by the end of 2023. The bus ratings would be exceeded due to the interconnections of new generation and transmission including the GridLiance West Upgrade (GLW) project.[2],[3] SCE, Los Angeles Department of Water and Power (LADWP) and NV Energy jointly own the Eldorado Substation and its equipment.
SCE proposes to split this existing Eldorado 230 kV bus into two sections and relocate lines to address the identified issues. The cost estimate for this project is $67 million. Because the equipment at the Eldorado Substation is jointly owned, the joint owners would share in the proposed project costs. LADWP and NV Energy propose to fund $18.2 million of the project costs, and CAISO ratepayers would fund the remaining project costs at $48.8 million.[4]
CAISO and SCE considered project alternatives that included a new substation and a higher-rated system at the Eldorado Substation. Both improvements have an estimated cost of $100 million. Other project alternatives were considered but were not recommended because they had limitations.
CAISO and SCE request comments on this proposed mitigation plan. Cal Advocates requests that CAISO and SCE provide additional information on their analysis to confirm the proposed solution and cost sharing agreement is the most cost-effective and just and reasonable option for CAISO ratepayers. The following are requests for specific information that were not included in 2022-2023 and 2023-2024 TPP materials.
- Confirm that the mitigation plan analysis considered the expected generation to interconnect at the Eldorado Substation in both the short and long-term.
SCE identified the need for this project as part of the reliability assessment for its high-voltage transmission system in the 2022-2023 Transmission Planning Process (TPP).[5] Therefore, Cal Advocates requests confirmation that the proposed transmission solution will accommodate the expected increase in interconnecting generation at the Eldorado Substation with the State’s 2023-2024 resource portfolios.
More specifically, the 2022-2023 TPP reliability study case assumed 1,506 megawatts (MW) of Full Capacity Deliverability Status resources, plus 300 MW of Energy Only resources, for a total of 1,806 MW resources seeking interconnection at the Eldorado Substation.[6] Of these resources, 1,198 MW (including out-of-state wind) were modeled at the Eldorado 500kV bus and the remaining 608 MW at the Eldorado 230kV bus.[7]
In contrast, the 2023-2024 TPP portfolios modeled 4,105 MW at the Eldorado Substation (with 3,176 MW of resources on the 500kV bus and 929 MW of resources on the 230 kV bus).[8]
- Confirm the mitigation evaluation timeframe.
The proposed mitigation plan to split the 230 kV bus appears reasonable if it will accommodate the expected energy flow for the next 10-20 years.
- Confirm the forecast short circuit duty in 10 years versus 25 years.
Does CAISO anticipate that another upgrade to the Eldorado Substation or that a new substation will be needed to accommodate the State’s resource portfolios within the next 10 years?
- Provide the impact of the interconnection of the proposed Southwest Intertie Project (SWIP)-North project at the Eldorado Substation. Specifically, provide the short circuit values before and after the SWIP-North project is interconnected.
- Provide confirmation on the just and reasonableness of the proposed project cost sharing agreement.
As mentioned, the equipment at the Eldorado Substation is jointly owned. The joint owners are pursuing generation and transmission interconnections at the Eldorado Substation, which are driving the need for a substation upgrade. The discussion so far has not identified the projects from LADWP and NV Energy that may be contributing to the project need. The information provided only mentions the CAISO’s transmission project, which is the Gridliance West upgrade. For this reason, Cal Advocates requests the following.
- Provide information on the generation or transmission projects (both generation or transmission owner and anticipated customers) that were considered in the short circuit studies that caused the breakers to overstress at the 230 kV and 500 kV buses.
- Provide the short circuit values before these transmission or generation projects are interconnected.
- Explain the difference between generation/transmission queue and operational queue. Please also identify the projects that were included in each of these queues for the short-circuit calculations. The CAISO presentation (slide #4) states: “the short circuit duty for the joint-owned Eldorado 230kV bus would be 75.3 kA by the end of generation/transmission queue and would be 64.2 kA by the 2023 operational queue.”[9] However, the CAISO does not explain the difference between the mentioned queues.
[1] Pub. Utilities Code, § 309.5.
[2] CAISO 2022-2023 Transmission Plan, CAISO, May 18, 2023 at p. 57.
[3] The GridLiance West Upgrade project was approved in the CAISO 2021-2022 Transmission Planning Process (TPP) cycle. This project was amended in the CAISO 2022-2023 TPP cycle.
[4] 2023-2024 Transmission Planning Process Eldorado 230 kV Short Circuit Duty Mitigation Project, June 28, 2023, CAISO, (CAISO presentation) at p. 7.
[5] CAISO 2022-2023 Transmission Plan, CAISO, May 18, 2023 at p. 57.
[6] Refer to the publicly available preferred system plan and portfolios for the 2022-23 Transmission Planning Process on the CPUC web site, Updated Mapping Dashboard Workbook – increase alignment with CAISO TPD, September 20, 2022, at the Mapping_bySub tab. 2019-2020 IRP Events and Materials (ca.gov)
[7] The Eldorado 500 kV substation includes a high voltage bus at 500 kV and low-voltage bus at 230 kV.
[8] Refer to the publicly available Portfolio and Modeling Assumptions for the 2022-2023 Transmission Planning Process, Final 2035 busbar Mapping dashboard, February 22, 2023 at Portfolios and Modeling Assumptions for the 2023-2024 Transmission Planning Process (ca.gov), BusbarDashboard2035_30MMT_HEBase_vD_02-22-23 at excel tab Mapping by Sub.
[9] CAISO Presentation at p. 4.