1.
Please provide a summary of your organization's comments on the March 24, 2026 DAME Configurable parameters implementation working group discussion.
The Public Advocates Office at the California Public Utilities Commission (Cal Advocates) appreciates the opportunity to comment on the California Independent System Operator Corporation’s (CAISO) March 24, 2026 meeting on CAISO’s Day-Ahead Market Enhancements (DAME) Configurable Parameters Implementation Working Group (Working Group).[1]
Cal Advocates provides the following comments on the Working Group:
- CAISO should seek to minimize ratepayer costs by adopting lower imbalance reserve (IR) requirements.
- CAISO should clarify renewable resource participation in imbalance reserve up (IRU) and consider impacts to California’s renewable policies. Specifically, CAISO should:
- Describe how renewable energy credit (REC) values are considered by CAISO in simulated IRU resource bid assumptions;
- Describe how RECs are treated in the calculation of opportunity costs that CAISO would pay to a resource awarded IRU but not dispatched by CAISO through the exercise of the IRU award;
- Clarify how CAISO’s lost opportunity cost (LOC) mechanism accounts for negative energy bids from resource adequacy (RA) capacity; and
- Clarify if CAISO considers any decreases in renewable generation caused by IRU awards to be renewable curtailments, and if so, explain how CAISO would categorize the curtailments in its curtailment records.
- CAISO should establish a “no later than” date to evaluate IR effectiveness and costs after the Extended Day-ahead Market (EDAM) launches.
CAISO imbalance reserve requirements will result in higher costs to ratepayers
CAISO IR requirements will be costly for CAISO Balancing Authority Area (BAA) ratepayers while not necessarily providing clear and quantifiable reliability benefits that CAISO BAA ratepayers need.[2] Cal Advocates agrees with SCE’s recommendation,
that the CAISO consider lower IR requirements for CAISO BAA in Phase One [of the EDAM launch], while allowing other regions to assess their own risk preferences based on local market structures and obligations.[3]
As SCE correctly points out, California has a “robust Resource Adequacy framework and corresponding must-offer obligations that already ensure substantial real-time capability.”[4] Due to the high ratepayer costs of IR and the risk that these costs are in fact unnecessary, CAISO should seek to minimize ratepayer costs by adopting the 75/25 percentile for IR requirements.[5] While the CAISO’s current plan[6] to implement 90/10 percentile levels instead of the original 97.5/2.5 IR procurement requirements when EDAM launches is an improvement, the 90/10 requirements are still too high for initial implementation. As soon as practical but within the first year of EDAM operations, CAISO should also adjust the IR procurement targets on a day-to-day basis, as residual unit commitment (RUC) adjustment is done today. CAISO has changed RUC adjustment policy to have lower adjustment levels on low-risk days.[7]
These high requirements have been accompanied with high IR prices, in the parallel operations market runs.[8] In response to the February 26, 2026 meeting of this Working Group, CAISO’s Department of Market Monitoring (DMM) stated that IR price results from recent simulations “do not seem consistent with the actual costs of providing the product.”[9] The CPUC Energy Division’s comments included analysis that estimates total annual IR costs of approximately $218 million.[10] Cal Advocates used data[11] provided in the Workshop Slides that used March 12, 2026 conditions to estimate annual cost impacts at different procurement/percentile levels for IRU and imbalance reserves down (IRD):[12]
|
Percentile scenario
|
IRU
($1000 per day)
|
IRD
($1000 per day)
|
Total
($1000 per day)
|
365 days of March 12 ($ million)
|
|
75/25
|
45
|
1
|
46
|
17
|
|
90/10
|
176
|
7
|
182
|
66
|
|
97.5/2.5
|
348
|
92
|
440
|
160
|
To add context to the cost impacts in the table above, The Brattle Group (Brattle) projected total annual EDAM benefits for the CAISO BAA from $148 million to $319 million.[13] Taking both those annual benefits and the IR costs at face value, the IR costs would significantly reduce the EDAM benefits for ratepayers in the CAISO BAA. Although CAISO has argued against the validity of any specific estimates of IR costs,[14] CAISO has not developed a cost-benefit study for the DAME products[15] and stakeholder estimates using CAISO data are the only current means to anticipate the costs of IR. In addition to the challenges of extrapolating from a small number of days, CAISO has objected that,
these estimates treat IR costs as purely additive. That is simply not accurate. Today, we already incur costs for similar services—hidden in uplift charges, real-time imbalance costs, and [resource adequacy] contracts.[16]
CAISO has not provided estimates of how these other costs would change or decrease, or how they compare to other effects, such as increases in the market-clearing price of energy.[17] In short, CAISO has not explained how any changes in uplift charges, real-time imbalance costs, and RA contracts would affect total IR costs. Therefore, stakeholders are unable to fully assess what the net cost of IR is and whether those costs would shift in the manner that CAISO suggests.
Given stakeholder concerns of high IR costs,[18] and the unclear reliability benefits that IR may provide, CAISO should adopt lower IR procurement requirements when CAISO launches EDAM in May 2026. CAISO’s proposal to use a 90/10 percentile and decreased parameter values fails to minimize ratepayer costs for IR.[19]
Bid design of imbalance reserve up for renewable resources
At the Working Group, CAISO showed simulated IRU bids from renewable resources up to approximately 5,000 megawatts (MW) in some hours,[20] and hourly IRU awards to renewables up to approximately 1,500 MW.[21] CAISO’s design of IRU co-optimizes the product with energy, meaning that a resource awarded a volume of IRU cannot simultaneously receive energy awards for that same volume.[22] The co-optimization of IRU and energy means that renewable resources[23] would curtail a portion of their generation equal to their IRU awards unless CAISO actually dispatches the resource through that IRU award. Such curtailment would cause the resource to not create RECs[24] that it otherwise would if it had received an energy award. As discussed below, Cal Advocates seeks clarifications from CAISO related to renewable resource IRU bidding assumptions and IR bid designs in general.
First, renewable resources that submit economic bids in CAISO markets typically bid at negative prices because their marginal costs are zero and their generation creates valuable RECs.[25] Since RECs created by renewable generation have value to the generator, the generator’s decision to bid for IRU could mean a loss of REC revenue if the resource does not generate.[26] The CAISO should: 1) describe how REC values are considered by CAISO in simulated IRU resource bid assumptions, and 2) describe how RECs are treated in the calculation of opportunity costs[27] that CAISO would pay to a resource that is awarded IRU but not dispatched by CAISO through exercise of the IRU award.
Second, the DAME Business Requirements Specification (BRS) describes CAISO’s calculation of LOC applied to certain RA resources that receive IRU awards.[28] The calculation isolates the RA capacity of the resource that receives the award and multiplies that volume by the day-ahead energy locational marginal price (LMP) decreased by the resource’s day-ahead bid price.[29] If a resource includes the negative value of a REC in its bid, this may cause the LOC calculation to exceed the energy LMP. CAISO should clarify that this interpretation of the BRS is correct; that if a renewable generator submits a negative economic bid equal to the negative value of a REC, the LOC will include that REC value via the negative bid.
Third, if a renewable resource is awarded IRU but is not dispatched by CAISO through that IRU award, it would not generate for the volume and market interval of the IRU award. CAISO maintains records of daily[30] and annual[31] curtailment activity, and the federal government tracks renewable curtailments with those reports.[32] CAISO should clarify if it considers decreases in renewable generation caused by IRU awards to be renewable curtailments. If so, CAISO should explain how it would categorize the curtailments in its curtailment records.
Lastly, CAISO should recognize economic and policy concerns related to reductions in renewable generation caused by IRU awarded to renewables. Although renewable curtailment occurs today on an economic basis, renewable resources could voluntarily bid for IRU and be consequently curtailed because of IRU design. Curtailments of renewables would slow California’s progress to meet RPS goals, may not be consistent with the state’s intent to encourage renewable generation,[33] and could increase the cost of the RECs that entities use to comply with California’s RPS program.[34]
[1] Slides for the meeting presentation are available online: CAISO, Day-Ahead Market Enhancements: Configurable Parameters Implementation Working Group Session #9, March 24, 2026 (Workshop Slides). Available at: https://stakeholdercenter.caiso.com/InitiativeDocuments/presentation-day-ahead-market-enhancements-dame-configurable-parameters-implementation-working-group-mar-24-2026.pdf.
[2] See California Public Utilities Commission (CPUC) Energy Division and Southern California Edison Company’s (SCE) comments submitted on March 12, 2026. CPUC Energy Division, Comments on 2/26 DAME Configurable Parameters Working Group, March 12, 2026 at Section 4. Available at: https://stakeholdercenter.caiso.com/Comments/AllComments/be123471-5b14-4d05-9128-f2a7ba0e229a#org-87c2b840-7ae1-4628-aa21-b192dc3fc08e; and SCE, Comments on 2/26 DAME Configurable Parameters Working Group, March 12, 2026 (SCE March Comments) at Section 4. Available at: https://stakeholdercenter.caiso.com/Comments/AllComments/be123471-5b14-4d05-9128-f2a7ba0e229a#org-43b4b934-4671-462a-a5eb-13ef9780c9c3.
[3] SCE March Comments at Section 4.
[4] SCE March Comments at Section 4.
[5] CAISO studied procurement volume and costs of IR at the 75/25 percentile requirement levels and found procurement levels were reduced with commensurate reductions in IR pricing. Workshop Slides at 60-73.
[6] Workshop Slides at 78.
[7] CPUC Energy Division, Comments on Day-Ahead Market Enhancements Configurable Parameters Implementation Working Group – Oct 21, 2025, November 10, 2025 (CPUC ED November Comments) at Section 5. Available at: https://stakeholdercenter.caiso.com/Comments/AllComments/7575843f-83b8-4baa-beb7-d042181dad1c#org-1b842753-f0d9-4c35-9ced-9ad5baca860f.
[8] Workshop Slides at 64.
[9] DMM also recommended caution when interpreting simulation results as they are based on unrealistic input data. DMM, Comments on 2/26 DAME Configurable Parameters Working Group, March 12, 2026 (DMM March Comments) at Section 1. Available at: https://stakeholdercenter.caiso.com/Comments/AllComments/be123471-5b14-4d05-9128-f2a7ba0e229a#org-8b156068-d9b9-4b68-bf5a-780c8e7b85a4.
[10] CPUC Energy Division, Comments on 2/26 DAME Configurable Parameters Working Group, March 12, 2026. Available at: https://stakeholdercenter.caiso.com/Comments/AllComments/be123471-5b14-4d05-9128-f2a7ba0e229a#org-87c2b840-7ae1-4628-aa21-b192dc3fc08e.
[11] To estimate costs, Cal Advocates digitized the y-axis graph values shown on Workshop Slides 61 and 64 to determine the market requirement prices and quantities of IR in the CAISO BAA for the percentile scenarios. These cost impacts are rough estimates since they reflect parallel operations results for the single day CAISO analyzed, March 12, 2026. Other days will have different market conditions.
[12] In the table, “Percentile scenario” refers to the three sets of percentiles for IRU and IRD requirements that CAISO analyzed for the CAISO BAA. The IRU/IRD “per day” columns are the total costs for the March 12 analysis, derived by multiplying IRU and IRD requirement volumes (bottom row of Workshop Slides at 61) by prices of IRU and IRD respectively (Workshop Slides at 64). The “Total” column is the sum of IRU and IRD costs on March 12. The “365 days of March 12” column multiplies the “Total” column by 365 to derive an approximate annual estimate.
[13] These are the “Baseline+” and “Split Market” scenarios previously provided by Brattle. Brattle, Preliminary Day-Ahead Market Impacts Study, January 24, 2025 at 25. Available as “261300” at: https://efiling.energy.ca.gov/Lists/DocketLog.aspx?docketnumber=24-IEPR-01.
[14] CAISO, Comment Responses – Day-Ahead Market Enhancements (DAME) Configurable Parameters Working Group – Dec 17, 2025, December 17, 2025 (CAISO December Comment Responses) at 3 and 7. Available at: https://stakeholdercenter.caiso.com/StakeholderInitiatives/Day-ahead-market-enhancements.
[15] Cal Advocates has repeatedly requested that CAISO conduct DAME product cost estimates in the course of CAISO’s development of DAME. See e.g., Cal Advocates, Comments on Draft Final Proposal, December 21, 2022 at Section 3. Available at: https://stakeholdercenter.caiso.com/Comments/AllComments/9ad17b1a-1975-490c-85f0-c52d3984e28e#org-e8f6879d-1e1a-49a2-aeba-cbcc41c4f6cd.
[16] CAISO December Comment Responses at 7.
[17] For example, CPUC ED November Comments at Section 4.
[18] In addition to the concerns raised by the Commission’s Energy Division, SCE, and DMM discussed above, Six Cities (CAISO December Comment Responses at 3), and Pacific Gas and Electric Company (CAISO December Comment Responses at 4) raised concerns of high IR costs.
[19] This position is consistent with the following statement from DMM:
DMM believes that starting go-live with lower requirements could protect against inefficiently high IR prices without creating much risk that uncertainty between day-ahead and real-time will be unable to be met. This would allow the ISO to gather and analyze market data to determine whether increasing the requirements is necessary for market efficiency and reliability.
DMM March Comments at Section 1.
[20] Workshop Slides at 33. The slides show a bid pattern consistent with solar production, rather than other types of renewables.
[21] Workshop Slides at 53.
[22] For example, a 50 MW resource that receives an IRU award of 30 MW for a market interval could at most only provide 20 MW of energy in the same interval. For further information on the co-optimization of IRU and energy, see CAISO, Day-Ahead Market Enhancements and Extended Day-Ahead Market, FERC Docket ER23-2686, August 22, 2023 at 49-55. Available at: https://www.caiso.com/Documents/Aug22-2023-DAME-EDAM-Tariff-Amendment-ER23-2686.pdf.
[23] Renewable resources, specifically wind and solar, are able to receive IRU awards. CAISO, Business Requirements Specification: Day-Ahead Market Enhancements Version 1.7, February 11, 2026 (CAISO DAME BRS) at 165. Available at: https://www.caiso.com/documents/business-requirements-specification-day-ahead-market-enhancement.pdf.
[24] Each 1 MW of renewable generation typically creates 1 REC. Load-serving entities and other entities in California use RECs to comply with the California Renewables Portfolio Standard (RPS). For more information, see: https://www.energy.ca.gov/programs-and-topics/programs/renewables-portfolio-standard/renewables-portfolio-standard-0.
[25] The negative bid may also include the value of any per megawatt-hour tax credits. DMM, Self-Schedules Bid Cost Recovery Allocation and Lower Bid Floor Draft Final Proposal, August 23, 2016 at 2-3. Available at: https://www.caiso.com/documents/dmmcomments_self_schedulesbidcostrecoveryallocation_bidfloor.pdf.
[26] Namely, this would occur if the renewable resource received an IRU award but is not actually dispatched by CAISO through that award in the real-time market.
[27] That is, the opportunity costs that are “drivers for setting” IR prices, rather than the opportunity cost calculation CAISO uses for the LOC component of overlapping RA capacity, described in the next paragraph. Workshop Slides at 25.
[28] CAISO DAME BRS at 98.
[29] CAISO DAME BRS at 98.
[30] Available at: https://www.caiso.com/library/daily-wind-solar-real-time-dispatch-curtailment-reports.
[31] Available at: https://www.caiso.com/library/production-curtailments-data.
[32] See data sources that the federal government uses: US Energy Information Administration, Solar and Wind Power Curtailments are Increasing in California, May 28, 2025. Available at: https://www.eia.gov/todayinenergy/detail.php?id=65364.
[33] See California Public Utilities Code at Sections 399.11(a) and 399.20(a)(1).
[34] Fewer RECs generated year to year would reduce the available supply of RECs to meet fixed RPS compliance targets. This would increase the value and price of RECs due to a scarcer supply of RECs.