Comments on EDAM Congestion Revenue Allocation - Phase 2 - February 23, 2026

Extended day-ahead market

Print
Comment period
Feb 24, 09:30 am - Mar 09, 05:00 pm
Submitting organizations
View by:

California ISO - Department of Market Monitoring
Submitted 03/09/2026, 04:17 pm

Contact

Aprille Girardot (agirardot@caiso.com)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

Comments on Extended Day-Ahead Market Congestion Revenue Allocation

Phase 2 Design Working Group Meeting - February 23, 2026

Department of Market Monitoring

March 9, 2026

Comments

The Department of Market Monitoring (DMM) appreciates the opportunity to comment on the Extended Day-Ahead Market Congestion Revenue Allocation Phase 2 Design Working Group Meeting – February 23, 2026.[1]

As has been pointed out by the Market Surveillance Committee and the Western Energy Imbalance Market expert, and recognized by the ISO and stakeholders, the interim congestion revenue allocation (CRA) can create incentives to self-schedule resources that can have detrimental market impacts. The interim CRA needs to be replaced as soon as practicable. The need to replace the interim CRA will only become more important as additional balancing areas join the Extended Day-Ahead Market (EDAM) and increase the potential for cross-BAA congestion impacts within the EDAM.

There may be several options to replace the interim CRA. Whichever option is chosen, the replacement allocation should not be tied to the actual schedules in the market—including schedules resulting from cleared economics offers. A congestion revenue allocation that depends on cleared schedules creates incentives for market participants to submit offers that are not consistent with their true marginal costs. This can undermine the purpose of the market and potentially lead to market dysfunction. Therefore, a core principle of any replacement, whether a short-term or longer-term replacement, should be that the congestion revenue allocation is not tied to cleared schedules in the EDAM.

 

 


[1] Extended Day-Ahead Market Congestion Revenue Allocation Phase 2 Design Working Group, California ISO, February 23, 2026: https://stakeholdercenter.caiso.com/InitiativeDocuments/Presentation-Extended-Day-Ahead-Market-Congestion-Revenue-Allocation-Phase-2-Feb-23-2026.pdf

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.

Please see the PDF attached below the final question for DMM's fully formatted complete set of comments. For the reader's convenience, the complete text of the comments is pasted in response to #1, but there may be some formatting errors.

3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

Please see the PDF attached below the final question for DMM's fully formatted complete set of comments. For the reader's convenience, the complete text of the comments is pasted in response to #1, but there may be some formatting errors.

DC Energy California, LLC
Submitted 03/09/2026, 01:23 pm

Contact

Justin Cockrell (cockrell@dc-energy.com)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

DC Energy understands that, currently, the CAISO is focused on analysis of unscheduled parallel flows specific to the pending PACE/PACW integration.  The CAISO must, however, continue to improve its understanding and modeling of unscheduled parallel flows on its system associated with all BAAs in the WECC.  This improved understanding and modeling is essential both for developing more accurate CRR auction models and other related CRR enhancements in the CAISO and for developing durable approaches to congestion revenue allocation and seams issues as EDAM expands and evolves. 

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.

As DC Energy stated in its prior comments, maintaining physical firm transmission rights and continuing to sell them in perpetuity conflicts with the other proposed draft principles.  Physical transmission rights have an inherent use it or lose it incentive that undermines economic dispatch. 

DC Energy is also concerned that physical firm transmission rights would continue to receive unduly discriminatory preferential priority in EDAM.  DC Energy requests greater clarity regarding how the continued sale of physical firm transmission rights could equitably coexist with financial transmission rights, particularly existing CRRs in the CAISO.  If physical transmission rights in other EDAM BAAs are bounded by a Simultaneous Feasibility Test, would they be rejected or curtailed if they consume CAISO transmission capacity that is constrained?  Would new physical transmission rights have to pay for their use of CAISO transmission capacity?  If there is insufficient transmission capacity leading to revenue inadequacy, would physical transmission rights be prorated or otherwise share in underfunding? 

If the answer to these questions is no, then the persistence of physical transmission rights in other EDAM BAAs will continue to be unduly discriminatory to CAISO transmission customers and CRR holders and distort day-ahead market outcomes.  If the answer to these questions is yes, then the transmission rights in other EDAM BAAs are essentially financial in nature and should be recognized as such.  The CAISO should facilitate a transition to the financial equivalent of firm transmission rights that are treated as the equivalent of existing CRRs for transmission customers in other EDAM BAAs in order to eliminate the self-scheduling incentive and ensure the equitable treatment of all transmission customers in EDAM.

These financial transmission rights could be allocated based in part on historic contract path flows, as occurred in the evolution of PJM and MISO, but there should be no point to point transactions with special priority in EDAM’s day-ahead market.  Because LMP markets, such as EDAM, presume the full use of the transmission grid on a network basis without point to point contract path transactions. 

Eventually, the CAISO should operate an integrated CRR process like it does today with allocations to transmission customers and residual capacity available via auctions based on simultaneous feasibility that price every constraint and ensure the maximum feasible use of the grid.  This would foster participation in the day-ahead market, provide price discovery as EDAM evolves, and reduce day-ahead congestion risk, ultimately reducing costs in the market, as well as allow the CAISO to jointly manage all day-ahead market congestion regardless of the EDAM BAA in which the congestion occurs. 

In the alternative, as an interim measure, the CAISO could rely on a transitional system of financial firm flow entitlements among EDAM BAAs to reduce self-scheduling incentives and address the inequitable treatment of CAISO transmission customers under the Phase I CRA design.  Eventually, however, financial firm flow entitlements should be a tool used to manage congestion revenue allocation across seams with non-EDAM BAAs only, because any intra-EDAM congestion should be managed centrally in the dispatch process.

3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

Shell Energy North America
Submitted 03/09/2026, 03:41 pm

Contact

Greg Macdonald (G.Macdonald2@shell.com)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

Shell Energy appreciates the opportunity to comment on this CRA presentation and acknowledges the hard work and analytical rigor that the CAISO has injected into this process in pursuit of designing a congestion revenue allocation that is equitable and robust. Shell Energy provides the following feedback and questions to inform the next steps.

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.
  • There are no timelines or milestones provided post May 2026. Please consider expanding to include the target policy development and implementation timelines.
  • Principle 1: “Congestion revenues should be allocated in an equitable manner so as to avoid undue cost shifts between EDAM BAAs”
    • The CAISO may consider defining metrics for equity in this context and explore a means to couple proposed methodologies more closely with cost causation i.e. BAA MCC allocations could be proportional to a transmission holders shift factor impact on the binding constraints or defining a threshold which cost shifts should not exceed, either at a customer or BAA level. This may be further expanded to reflect the causal contribution of transactions to binding constraints such that it captures and accounts for parallel flow impacts across BAA boundaries.
  • Principle 2: "Supports the ability of transmission customers with firm transmission rights or CRRs to manage and hedge congestion risk exposure considering grid conditions and feasibility of flow"
    • Strongly agree. Consider the inclusion of conditional firm transmission rights as a firm right. This should arguably take the place of principle 1 as the highest priority item. Without a means to meaningfully hedge congestion exposure/risk in the EDAM, entities will often default to submitting self-schedules, which will implicate market efficiency and complicate hedging strategies.
  • Additional Principles:
    • The CAISO may consider addressing revenue adequacy, both for CAISO CRRs and non-CAISO EDAM OATT customers. 
    • Given that the scope of the analysis has been focused on the interactions between PAC/CAISO, it may be worth ensuring that a target design is robust and efficiently scalable to a broader EDAM footprint.
3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

Six Cities
Submitted 03/10/2026, 03:32 pm

Submitted on behalf of
Cities of Anaheim, Azusa, Banning, Colton, Pasadena, and Riverside, California

Contact

Margaret McNaul (mmcnaul@thompsoncoburn.com)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

The Six Cities note the clarifications provided by the CAISO during the February 23rd meeting related to the Stage 1 analysis, and also note the CAISO’s presentation of additional information regarding the cost estimate of the potential impacts of the congestion revenue allocation as discussed during the March 6th Market Surveillance Committee meeting.  As shown by the data, which the Six Cities agree has certain limitations because it is necessarily based on historic information and is premised on certain assumptions that may not accurately represent outcomes once the Extended Day Ahead Market (“EDAM”) and Day Ahead Market Enhancements (“DAME”) are operational, transactions in PacifiCorp have a larger impact on CAISO congestion than transactions in the CAISO have on PacifiCorp.  In the Six Cities’ view, this supports the need to address the asymmetry in allocation of congestion revenues due to parallel flows for the CAISO balancing authority area (“BAA”).  The Six Cities therefore support the CAISO’s clear scoping of this topic within the Phase 2 initiative.

The CAISO’s limiting of its analysis to only the EDAM go-live footprint is concerning.  For example, the CAISO has stated it does not, at this time, intend to provide analysis that examines the impacts of its congestion revenue allocation policy on parties other than the CAISO and PacifiCorp and that it is keeping its analysis “very targeted.”  (See Feb. 23 presentation at 14.)  The CAISO explains that it “remains committed to provide analytics to support” policy development in the Congestion Revenue Requirements (“CRR”) Enhancements and EDAM Congestion Revenue Allocation initiatives (id.).  The Six Cities encourage the CAISO to be responsive to stakeholder requests for additional analysis, including requests for information about possible impacts to CRR revenue adequacy and the auction process so that this information is available to inform the upcoming working groups in this initiative and an eventual resumption of activities in the CRR Enhancements initiative.  Stakeholders would not be requesting this information if they did not think it was relevant to upcoming policy discussions. 

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.

The Six Cities generally support the proposed design principles.  The inclusion of additional language in the design principle related to avoidance of cost shifts is noted and appreciated, and the Six Cities believe that this addition is sufficient to address their concern.  The Six Cities’ primary concern in suggesting additional language related to the allocation of congestion revenues as between BAAs, including the CAISO BAA, was to ensure focus on addressing asymmetries present in the current design. 

3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

At this time, the Six Cities do not have topics to present during the workshops, but expect to participate actively through discussions and comments.

Southern California Edison
Submitted 03/09/2026, 03:53 pm

Contact

Stephen Keehn (stephen.keehn@sce.com)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

SCE appreciates the efforts of the CAISO to provide stakeholders with an update on the CAISO’s analysis, although SCE is not able to comment on the analysis since it has only been released for the MSC meeting from last Friday. SCE recommends that CAISO also seek comments on the results presented to the MSC after allowing stakeholders an appropriate amount of time to digest and understand the results presented. 

SCE appreciates the limits of analysis performed before EDAM go-live but urges CAISO to conduct additional analysis on an expanded EDAM market with more participants beyond just CAISO and PacificCorp. This information will be useful in determining the Phase 2 design, and it seems very likely that at least PGE will join EDAM before the Phase 2 design is implemented. The initial analysis as reviewed in the presentation indicates that transactions in CAISO and PacifiCorp have small potential loop flow congestion impacts in the other regions. This provides a level of comfort for the initial implementation of EDAM, but it is important to understand if this initial finding will continue when EDAM expands. Since much of this analysis will rely on the currently available EIM data, there doesn’t seem to be any benefit to waiting to start analyzing this data.

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.

SCE’s previous comments indicated that the principles should not preclude a possible design that has all EDAM BAA using financial transmission rights, similar to the CAISO’s CRRs. While SCE was glad to see that a bullet was added that indicates the principles do not “preclude consideration of financial transmission rights/CRRs which can be made compatible with continued OATT sales” this doesn’t fully convey what SCE and others were seeking. The possible solution that SCE wanted to be able to be considered would not create the FTRs to be compatible with continued OATT sales, but would have the FTRs replace OATT sales in all EDAM BAAs. As SCE commented last time, this might not be the selected solution, but the principles should not exclude it as a possibility.  

3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

The Energy Authority
Submitted 03/09/2026, 01:05 pm

Contact

Dan Williams (dwilliams2@teainc.org)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

The Energy Authority (TEA) found the EDAM Congestion Revenue Allocation (CRA) Phase 2 (CRA-2) working group presentation to be a useful recap of submitted stakeholder comments but is looking forward to getting into substantive discussions as soon as possible, following final revisions and additions to the principles. TEA appreciated the CAISO Market Surveillance Committee (MSC) meeting on March 6, 2026, which included updated analysis that more clearly highlighted the risks of operating EDAM under the existing CRA model and had engaging discussion around design alternatives and issues that need to be addressed with the current CRA design. 

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.

Revise the first principle to say: "Congestion revenues should be allocated in an equitable manner so as to avoid undue cost shifts between EDAM BAAs and within EDAM BAAs."

EDAM BAAs do not fund EDAM Transmission Service Providers' (TSP) transmission revenue requirement. EDAM Entity TSPs' Network Transmission (NT) customers are responsible for shouldering the revenue requirement, after accounting for the total contribution of Point-to-Point (PTP) customer transmission revenues. It is those two types of customers that are ultimately allocated the congestion revenues collected by CAISO and returned to the EDAM Entities under the current CRA policy, or credited directly to the customers themselves. It is just as important that CRA-2 policy provides a framework that allows for accurate, transparent, equitable allocation at the customer level as it is that the allocation is equitable at the BAA level. During the meeting, TEA noted that existing non-CAISO EDAM TSP Tariff provisions are directionally incompatible with existing CRA policy in that NT customers will frequently be ineligible to receive Tier One congestion allocation due to their reliance on 6-NN rights, i.e., non-firm network, despite being allocated their share of their TSP's annual transmission revenue requirement the same whether scheduling on 7-FN or 6-NN rights. TEA believes there are immediate and longer-term enhancements that could be made to address this narrow but impactful issue and requests that this principle be revised to ensure asymmetries in sub-allocation between customer clasess are not overlooked.

 

Revise the second-to-last principle to say: "Provides a comparable allocation method for the CAISO balancing area with a CRR construct and for EDAM balancing areas which sell firm OATT transmission that is based on holding the rights rather than using the rights." 

CAISO's Congestion Revenue Rights (CRR) market does not require a CRR holder to schedule energy transfers or otherwise "use" the CRR source-sink path represented by the CRR in order to receive congestion revenue or be assigned revenue uplift. The CRA policy does the opposite. Non-CAISO EDAM area transmission rightsholders must schedule on their rights in order to receive direct congestion revenue allocation through the Tier One reversal process. This fundamentally undermines the value of investing in or owning these rights and distorts allocation between NT and PTP rightsholders given the nature of PTP vs. NT billing determinants. CRA-2 policy cannot provide a "comparable allocation" between the CAISO area's CRR construct and the non-CAISO EDAM areas' OATT-based construct unless it addresses this current asymmetry and TEA therefore requests the principle be revised to ensure it is.  

 

Add a principle that reads: "Supports efficient, reliable scheduling of bilaterally-contracted Firm energy transfers between and within regions and markets."

EDAM is not an ISO/RTO market with a common RA program and must-offer obligation or common Tariff, and EDAM's existence does not change many aspects of the CAISO market, including its RA/RPS programs, AS optimization, use of convergence bids, access to a robust and liquid intertie market, and various other unique programs that do not currently extend to the non-CAISO EDAM areas.

EDAM is instead a novel hybrid organized market that maintains separate BAAs and includes a financially-binding RSE program that requires all Load Serving Entities (LSE) to forward contract with resource owners such that on any given day each LSE within a non-CAISO EDAM BAA can meet its RSE obligation. This is challenging given that RSE obligations fluctuate day-to-day based on load forecast estimates and historical estimates of DA-to-RT uncertainty, and given that LSEs must also navigate planned and forced outages, fuel availability, and other factors that influence their supply portfolios. The EDAM footprint is not structurally oversupplied, nor does it have the plurality of sellers necessary to ensure liquid and competitive contracting among resources within EDAM's footprint. 

EDAM therefore MUST have policies that allow for efficient, reliable bilateral contracting for Firm energy transfers from outside EDAM's footprint in the pre-DAM window, ranging from as little as an hour prior to the IFM run each day to days, weeks, months, or years in advance.

The current CRA fails to meet this need, especially for the non-CAISO areas, and exposes EDAM LSEs to undue financial risk. Under the current CRA, LSEs must deal with the lack of open economic intertie bidding at non-CAISO EDAM BAA borders, the cumbersome nature of Designated Network Resource (DNR) registration required to receive Tier One eligible 7-FN rights, and the lack of Tier One eligible 7-F PTP rights available on non-CAISO EDAM systems - and even when they can overcome these hurdles, must make an untenable choice between forgoing the potential benefits of economic dispatch and ring-fencing their price-risk through self-scheduling their supply resources. Further, the existing CRA adds unnecessary complexity to effecting interregional transfer of Firm energy with certain capacity attributes, such as RA- and RPS-qualifying capacity.

It is imperative that the CRA-2 initiative addresses these flaws and supports contracting of uncommitted supply from adjacent bilateral markets. It is also imperative, however, that as adjacent organized markets are implemented, including SPP's RTOE that goes live before EDAM and SPP's Markets+ that goes live the year following, EDAM LSEs are still able to contract efficiently with uncommitted supply located in either of those two markets. More changes are required here than fit within the scope of CRA-2 but it will still be important to address the role congestion revenue allocation plays in resolving seams issues associated with scheduling energy between regions and markets.

Last, there is a basic reciprocity issue that was overlooked when current CRA and EDAM policy was set that must be addressed in this CRA-2 initiative. CAISO's existing intertie and CRR markets, including as they will be updated with the changes filed with FERC in its EDAM/DAME Tariff Clarifications, ensure that CAISO LSEs have the tools they need to efficiently and reliably contract with uncommitted capacity from outside the CAISO BAA, whether that capacity is in a WEIM-only area or in a non-CAISO EDAM area. LSEs in the non-CAISO EDAM areas must be afforded the same, including the ability to contract with uncommitted Firm energy and capacity in the CAISO area for export to an EDAM area on a forward basis. Similar to the last point above, TEA recognizes there are issues here that extend beyond congestion revenue allocation. However, as those issues are addressed, reciprocal congestion revenue allocation issues will also need to be addressed. It follows that consideration of them should fit within the scope of this initiative, which requires the addition of the principle TEA requests here.

TEA below requests an opportunity to expand on these comments through a stakeholder presentation at a future meeting.  

3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

TEA requests an opportunity to present a fuller description of each of the principles-based issues identified above and what it views as near- and long-term solutions that could be applied at both the CAISO and non-CAISO EDAM Entity levels.

Wyoming Office of Consumer Advocate
Submitted 03/09/2026, 03:16 pm

Contact

William Achi (william.achi@wyo.gov)

1. Please provide your organization's overall feedback regarding the Extended Day-Ahead Market (EDAM) Congestion Revenue Allocation - Phase 2 working group presentation held on February 23, 2026.

The Wyoming Office of Consumer Advocate (OCA) appreciates the opportunity to provide comments on the EDAM Congestion Revenue Allocation (CRA) Phase 2 working group meeting. Regarding the Phase 1 analysis discussion, the OCA appreciates both the California ISO’s (CAISO) efforts to provide additional clarity on the Stage 1 analysis and the structural congestion conditions inherent to the EDAM market footprint and the CAISO’s commitment to continue providing analysis to support the ongoing development of the CRA design. While the OCA understands some of this information will be presented through other forums, such as the Market Surveillance Committee, the OCA encourages the CAISO to continue presenting Stage 2 and Stage 3 analysis findings directly to this working group as they become available. Doing so will afford stakeholders the greatest opportunity to understand the impacts of the revised CRA methodology and to make informed and meaningful contributions to the Phase 2 design process.

Regarding the proposed timeline for the upcoming design workshops, the OCA generally supports the proposed approach of holding four working group sessions between March and May 2026. The OCA believes that closely-spaced meetings help stakeholders remain focused on the substantive issues and maintain momentum to build effectively on prior discussions. However, the OCA has concerns about whether the broader Q4 2026 decision timeline provides sufficient time to develop a sound long-term design. The Phase 1 EDAM CRA Final Proposal contemplated a 12-to-24-month stakeholder process, with near-term enhancements to be considered within or shortly after the first full year of EDAM operations in 2027.

The OCA acknowledges and takes seriously the concerns raised by both CAISO staff and stakeholders that the current interim design may create perverse incentives for self-scheduling and potential market gaming. The OCA agrees that close monitoring of these issues is essential and that near-term enhancements should be pursued promptly if such concerns materialize in actual market operations. That said, the OCA cautions that the focus on near-term concerns should not come at the expense of a thorough and well-considered long-term design, and the OCA encourages the CAISO to remain flexible on timing should the working group process indicate that additional deliberation is warranted.

2. Please provide any additional feedback regarding the associated principles for guiding Phase 2 design.

The OCA appreciates the CAISO’s responsiveness to stakeholder comments submitted following the December 11, 2025, working group meeting, and recognizes the efforts made to incorporate that feedback into the updated presentation of the Phase 2 design principles. The OCA generally supports the design principles as previously introduced and welcomes the additions and clarifications reflected in this meeting.

With respect to the principles supporting the continued administration of Congestion Revenue Rights (CRRs) in the CAISO balancing area and the continued sale of OATT transmission rights, the OCA appreciates the CAISO’s sustained commitment to a design framework that is compatible with and creates a comparable allocation method for both approaches. The OCA understands that some stakeholders have expressed a preference for a market-wide CRR-like design as an end goal for the entire EDAM footprint. While the OCA recognizes the merits of that perspective, the OCA cautions against a design approach that would effectively compel a significant transformation in how transmission rights are structured and administered across the Western Interconnect. The OCA therefore supports the current design framework that preserves optionality and does not foreclose existing OATT-based approaches in favor of a singular, market-wide construct.

The OCA also strongly supports the principle providing transparency into market footprint congestion. Access to clear and meaningful congestion data is essential not only to enable market participants to make informed decisions regarding their congestion cost exposure, but also allow state regulators to understand and evaluate the impacts of EDAM congestion on the entities they regulate.

3. Please provide any additional feedback including whether your organization would be interested in presenting and introducing any congestion revenue allocation design concepts for consideration at the upcoming workshops. You may provide this feedback either through this comment template or you may email isostakeholderaffairs@caiso.com.

The OCA does not anticipate presenting an alternative congestion revenues allocation design concept at this time. However, the OCA looks forward to continued participation in the upcoming design workshops and remains committed to providing meaningful feedback as design alternatives are introduced and evaluated by the working group.

Back to top