COMMENTS OF B3K PROSPERITY
ON THE PRELIMINARY RELIABILITY STUDY RESULTS FOR THE PG&E KERN AND TEHACHAPI & BIG CREEK CORRIDOR STUDY AREAS
CALIFORNIA INDEPENDENT SYSTEM OPERATOR — 2026-2027 TRANSMISSION PLANNING PROCESS
Submitted via: Better Bakersfield and Boundless Kern (“B3K”), through the Advanced Energy Leadership Advisory Council (AELAC)
Submitted to: California Independent System Operator Corporation Infrastructure Development; Regional Transmission
Re: Comments on the preliminary reliability study results posted August 14, 2026 (document dated August 15, 2026), and on the material presented at Stakeholder Meeting #2, September 23-24, 2026, as they concern the PG&E Kern and Tehachapi & Big Creek Corridor study areas.
Better Bakersfield and Boundless Kern (B3K), through its Advanced Energy Leadership Advisory Council (AELAC), submits these comments pursuant to the comment opportunity established in the 2026-2027 Transmission Planning Process (“TPP”) schedule for material presented at Stakeholder Meeting #2. These comments are directed to the preliminary reliability study results for the PG&E Kern study area and, secondarily, to the Tehachapi & Big Creek Corridor study area. They are based on publicly posted CAISO, CPUC, and CEC material, which is identified in the source list at the end of this letter.
I. SUMMARY OF COMMENTS
The preliminary results identify significant modeled thermal overloads, voltage deficiencies, and stability concerns within the Kern-area transmission system under multiple planning scenarios and contingencies, with several conditions becoming more severe as modeled demand increases. In addition, Kern County stakeholders are aware of significant prospective load growth associated with industrial, commercial, and economic development projects that may not yet be fully reflected in utility energization requests or the planning baseline.
The severity of a substantial number of the identified violations increases under the 2031 Summer Peak High CEC Forecast sensitivity relative to the baseline case. B3K/AELAC views these results as warranting particular attention to Kern County load-serving capability. The resource portfolio for this cycle holds the PG&E Kern study area flat between 2036 and 2041, so the questions Kern County brings to this cycle are principally questions about serving load. B3K/AELAC respectfully request the following:
1. That CAISO select and identify mitigations, in the final reliability study results due October 30, 2026, for the Kern-area findings presently carried as “Under Review,” and in particular for Midway-Gates 230 kV, Kern-Magunden 70 kV, and San Bernard-Weedpatch 70 kV.
2. That CAISO confirm whether the scope of the Midway 115 kV Bus Upgrade (2526-R-08), as approved in the 2025-2026 Transmission Plan, resolves the additional Kern-area findings now assigned to it in this cycle, including under the high demand forecast; and that CAISO confirm the scope, sizing basis, and anticipated in-service dates of the Wheeler Ridge Junction and Tejon Area Reinforcement projects.
3. That the detailed engineering analysis of Path 15 and Path 26, deferred from the 2025-2026 cycle into this cycle, be performed and reported in this cycle; that its scope include the Midway 115 kV and 230 kV terminal configuration; and that CAISO state how it will treat the two Kern- and Path 15-related economic planning study requests identified in the Study Plan.
4. That CAISO treats the 2031 Summer Peak High CEC Forecast case as a planning case for the Kern area instead of as a sensitivity, given the number of Kern findings that bind more severely in that case.
5. That CAISO and the affected Participating Transmission Owners confirm which Kern County load additions are reflected in the local-area reliability baseline through the Energy Commission’s “Known Loads” modifier and identify what documentation would be required for additional loads to be reflected in the next baseline.
6. That CAISO indicates whether the Cal Flat-Gates 230 kV constraint receives any assessment in this cycle, in light of the resource remapping between the PG&E Kern and PG&E Fresno study areas described in the CPUC’s final busbar mapping report for this cycle.
II. KERN COUNTY IS DIVIDED BETWEEN TWO STUDY AREAS
Kern County is served by two Participating Transmission Owners and appears in the TPP as two of the eighteen study areas identified in Section 2.3 of the Study Plan. Western and northern Kern County, including Bakersfield, Midway, and Buttonwillow, is within the PG&E Kern local study area. Eastern and southern Kern County, including Tehachapi, Mojave, Rosamond, and the associated wind fleet, is assessed within the SCE Tehachapi and Big Creek Corridor local study area.
B3K/AELAC requests that CAISO characterize Kern County load-serving capability across both study areas rather than solely within each area in isolation.
III. COMMENTS ON THE PRELIMINARY RELIABILITY RESULTS
A. The Kern-area findings are demand-driven.
CAISO studied the PG&E Kern area across six baseline scenarios (2028, 2031, and 2036 summer peak; 2028 and 2031 spring off-peak; and 2036 summer off-peak) and three sensitivities, including a 2031 Summer Peak High CEC Forecast case representing higher demand growth. The results identify thermal overloads on nineteen 70 kV, 115 kV, and 230 kV facilities, low-voltage conditions at eighteen substation buses across sixteen substations, and potential WECC/NERC transient stability criteria violations under six separate contingencies.
The Midway-Gates 230 kV line loads to 125 percent in 2028 and 131 percent in 2031 under baseline demand, and to 141 percent under the 2031 high demand forecast. The same pattern appears across the following systems:
|
Facility
|
Worst-case baseline
|
2031 High CEC forecast
|
Stated disposition
|
|
Midway-Gates 230 kV
|
131%
|
141%
|
Under Review
|
|
Midway-Tupman-Rio Bravo-Renfro 115 kV
|
129%
|
132%
|
Midway Bus Upgrade
|
|
Semitropic-Famoso 115 kV
|
126%
|
129%
|
Under Review
|
|
Wheeler Ridge-Lakeview 70 kV
|
116%
|
120%
|
Under Review
|
|
Kern PP-Westpark #1 115 kV
|
111%
|
113%
|
Under Review
|
Source: PG&E Kern preliminary study results. Worst-case baseline is the highest loading across the six baseline scenarios.
B3K/AELAC do not dispute that worst-case and High CEC values are often driven by different binding contingencies, and that a lower High CEC figure for a given facility therefore does not indicate that higher demand improves that facility’s performance. For the facilities listed above, the high demand forecast produces the more severe result, and those facilities are concentrated on the corridors that would serve new load in the Bakersfield and Midway areas.
B. Severe findings carry no selected mitigation.
The severe thermal findings in the Kern area, and the most demand-sensitive one, are recorded as “Under Review”:
|
Facility
|
Worst-case loading
|
Contingency and year
|
|
Kern-Magunden 70 kV
|
452%
|
P7 double-circuit tower line, 2028 summer peak
|
|
San Bernard-Weedpatch 70 kV
|
334%
|
P6 (N-1-1), 2028 summer peak
|
|
Midway-Gates 230 kV
|
131% base / 141% high
|
P1 (N-1), 2031 summer peak
|
We note that the San Bernard-Weedpatch 70 kV also carries a 325 percent finding under a P7 double-circuit tower line outage that is assigned to the Wheeler Ridge Junction project; the 334 percent has no noted mitigation. Then, on the Kern-Magunden 70 kV contingency that produces the 452 percent result in 2028, the 2031 Summer Peak case is recorded as non-converged. The Kern County Parties request that CAISO report the 2031 result for that contingency in the final study results, since a non-converged case for this facility leaves the 2031 condition unquantified.
More generally, B3K/AELAC request that the Kern-area findings presently carried as “Under Review” receive a stated disposition in the final reliability study results due October 30, 2026, rather than being carried forward to a subsequent planning cycle. Where CAISO concludes that no mitigation is warranted, B3K/AELAC request that the basis for that conclusion be stated, including the demand level at which the finding would become actionable.
C. Low-voltage findings.
Eighteen substation buses at sixteen substations in the Kern area fall below the 0.9 per-unit planning standard under at least one studied condition. The lowest recorded values include Tejon 70 kV and San Bernard 70 kV at 0.58 per unit; Kern Ridge 115 kV, Temblor 115 kV, and Wheeler Ridge 115 kV and 70 kV at 0.59; Magunden 70 kV at 0.61; and Arvin 70 kV at 0.63. The complete list is at Attachment B.
Several of these findings are dispositioned “sensitivity only” or “continue to monitor.” B3K/AELAC request that CAISO identify, for each such finding, the load level or system condition at which the finding would move from monitoring into mitigation.
D. Transient stability at Midway.
The transient stability assessment for the Kern area was performed across a reduced scenario set of four baseline scenarios (2028 spring off-peak, 2031 and 2036 summer peak, and 2036 summer off-peak) and two sensitivities. Within that set, the preliminary results identify potential WECC/NERC criteria violations for an internal fault at bus-tie breaker 302 on Midway 115 kV Bus 1D; for an internal fault at bus-tie breaker 392 on Midway 115 kV Bus E; and for a fault on Midway-Wheeler Ridge 230 kV circuits 1 and 2, the last of which produces violations in all four baseline scenarios. Each is recorded as under review. Violations are also identified for non-redundant relay and battery failures at Westpark 115 kV, Corcoran 115 kV, and Kern Oil substation 115 kV, of which the first two have identified mitigations consisting of a redundant relay and a redundant battery supply respectively.
B3K/AELAC notes that the Midway-Wheeler Ridge 230 kV finding does not appear under the high demand sensitivity and advance it as a location-driven finding. Given that CAISO has stated that the need for upgrades on Path 15 and Path 26 has been established, and given that the detailed engineering for those upgrades was deferred into the present cycle, B3K/AELAC request that the Midway stability findings be resolved in this cycle and that their resolution be coordinated with the Path 15/26 engineering analysis.
E. Findings which do not support Kern County’s position.
In the interest of an accurate record, B3K/AELAC note two findings that do not support the position advanced in this letter. The preliminary results state that “no single contingency resulted in total load drop of more than 250 MW” and that there is “no single source substation with more than 100 MW” in the Kern area. Read together with the thermal and voltage results, the Kern system appears to be stressed at the facility level. B3K/AELAC do not characterize the Kern area as a bulk-system reliability emergency. The concern raised is the capability to reliably accommodate anticipated incremental load growth.
IV. LOAD NOT PRESENTLY REFLECTED IN THE BASELINE
As CAISO states on its Large Loads program page, “The ISO does not study load interconnections, but accounts for these loads in using the CEC’s demand forecast for study assumptions, forecasts, and network models.”
For the 2026-2027 cycle, the Study Plan provides that local area reliability studies and long-term local capacity requirement studies use the 2025 California Energy Demand Update Forecast 2025-2045, adopted by the Energy Commission on January 21, 2026, including the Known Loads load bus modifiers. CAISO’s stated rationale is that this “aligns local area transmission planning with utility distribution planning which already uses known loads to allow ample lead time for potential transmission upgrades.” The Known Loads modifier is applied to local area reliability studies; the Study Plan provides that the economic, policy, and bulk system peak studies continue to use the 2024 IEPR planning forecast. The PG&E Kern study area is a local area study, and is therefore one of the places in this cycle where documented Kern County load would register. As Section VII notes, it is also, on the current portfolio, the principal place where a Kern-area need can still be identified.
B3K/AELAC therefore raise the following, acknowledging that part of it is addressed to the Participating Transmission Owners and to the Energy Commission rather than to CAISO:
1. That CAISO or the affected Participating Transmission Owners confirm which Kern County load additions were reflected in the local-area reliability baseline for this cycle through the Known Loads modifier, at which substations, and in which study years.
2. That CAISO identify what documentation would be required for load additions to be reflected in the baseline for the next planning cycle.
V. COMMENTS ON STUDY ASSUMPTIONS
The observations in this section concern the demand forecast and the resource portfolio rather than the reliability results. They are offered because the portfolio determines whether a Kern-area need can be recognized on the generation side, and the results discussed in Section III describe the condition of the system that would serve new load. It is the second of these that B3K/AELAC is concerned with, and the observations below are intended to explain why.
1. High demand forecast: The Study Plan describes the 2031 Summer Peak High CEC Forecast sensitivity in which load is increased by turning off Additional Achievable Energy Efficiency. Because a substantial share of the Kern-area findings bind more severely in that case, B3K/AELAC requests that CAISO treat it as a planning case for the Kern area instead of a sensitivity or alternatively state the criteria under which a sensitivity result is carried into mitigation selection.
2. Resource portfolio: Table 19 of the CPUC’s final Resource-to-Busbar Mapping and Other Modeling Assumptions Report for this cycle maps 14,284 MW to the PG&E Kern study area in the 2036 base portfolio and the identical figure, 14,284 MW, in 2041. At that level, PG&E Kern is the largest single study area in the 2036 base portfolio. PG&E Kern and SCE North of Lugo are also the only two study areas in the base portfolio that show no growth across the final five years of the planning horizon; every other area grows between 8 and 150 percent. B3K/AELAC raises this not to seek a larger allocation, but because the flat figure is what leaves the load-serving questions in Sections IV and V as the substance of Kern’s interest in this cycle. B3K/AELAC requests that CAISO state whether the flat figure reflects a modeled completion of build-out by 2036 or a consequence of the busbar mapping methodology, and that B3K/AELAC be advised if a portfolio update in this cycle changes it.
3. Composition of the PG&E Kern zone figure. B3K/AELAC notes that the PG&E Kern busbar-mapping zone is not coterminous with Kern County, and that the same report shows that 2,924 MW of the 14,284 MW total is Morro Bay offshore wind mapped to the Diablo Canyon 500 kV substation, which is not in Kern County. B3K/AELAC requests that CAISO, in any Kern-area assessment in this cycle, distinguish resources mapped within Kern County from resources mapped elsewhere in the PG&E Kern study area, and do not equate the zone with the county.
4. Exceedance analysis. The report states that resources mapped in 2036 to the Fresno and Kern study areas “result in 5 constraint exceedances and the possibility of corresponding triggered upgrades only in Fresno and not Kern,” that “no additional exceedances are observed in 2041,” and that “as in the 25-26 cycle model years, no exceedances are shown in PG&E Kern.” B3K/AELAC does not dispute that finding, and request that CAISO identify what load or resource documentation would cause a Kern-area constraint to be recognized in that analysis.
5. Resources remapped between study areas. The report notes that resources were remapped from buses in the PG&E Kern area “to better align with other criteria and to limit the exceedance on the Cal Flat-Gates 230 kV line, which has an identified White Paper upgrade with an estimated cost of $1,008 million,” and that those resources, 940 MW, “were placed in PG&E Fresno.” B3K/AELAC understands remapping of this kind to be a routine part of the busbar mapping methodology. B3K/AELAC wishes to clarify whether the Cal Flat-Gates 230 kV constraint receives any assessment in this cycle, and whether the remapping has any bearing on transmission need identified in or near the Kern study area.
VI. RELATIONSHIP TO OTHER SUBMISSIONS IN THIS CYCLE
These comments address CAISO’s preliminary reliability study results, they do not propose a transmission or non-transmission solution and are not submitted through the Request Window closing October 15, 2026.
VII. KERN COUNTY AND ENERGY EQUITY
Kern County hosts wind, solar, geothermal, storage, and transmission infrastructure that serves the State as a whole.
- Kern County is the largest electricity-producing county in California and one of the largest in the United States.
- Kern County has approximately one million residents, and its county seat, Bakersfield, is the ninth-largest city in California.
- Electricity produced in Kern County is delivered into the CAISO-controlled grid, which serves approximately 32 million consumers.
- Over the most recent 12-month period, power plants in Kern County generated nearly 35 terawatt-hours of electricity, well in excess of the County’s own consumption of around 6 terawatt-hours.
- Approximately 18.6 percent of Kern County residents live below the poverty line, and many communities experience significant air-quality and environmental burdens. (OEHHA).
B3K/AELAC requests that the planning process recognizes both Kern County’s role as a major energy-producing region and its emerging need for reliable transmission capacity to support local industrial and economic growth. B3K/AELAC recognizes that workforce development, community benefits, and broader economic-development considerations extend beyond CAISO’s direct transmission-planning authority. Nevertheless, where transmission investments are required in communities that host significant portions of California’s energy infrastructure, B3K/AELAC encourages coordination among CAISO, state agencies, utilities, and local stakeholders so that reliability planning supports both statewide energy objectives and sustainable regional economic development.
IIX. CONCLUSION
B3K/AELAC appreciates the opportunity to comment and request that the matters raised in Section I be addressed in the final reliability study results due October 30, 2026. Overall, B3K/AELAC note the complexity of the analysis and decision making, the time and respect provided in prior meetings and dialogue, and the continued opportunity to further engage in long-term planning of power resources in our region.
ATTACHMENT B
Kern-Area Findings, Preliminary Reliability Study Results
All values from the PG&E Kern preliminary study results posted August 14, 2026 (document dated August 15, 2026).
Table B-1. Thermal overload findings
|
Facility
|
Worst-case baseline
|
2031 High CEC
|
Stated disposition
|
|
Kern-Magunden 70 kV
|
452%
|
129%
|
Under Review
|
|
San Bernard-Weedpatch 70 kV
|
334%
|
111%
|
Under Review / Wheeler Ridge Junction
|
|
Weedpatch-Magunden 70 kV
|
195%
|
—
|
Wheeler Ridge Junction
|
|
Taft-Maricopa 70 kV
|
178%
|
146%
|
Midway Bus Upgrade / Under Review
|
|
Taft-Elk Hills 70 kV
|
163%
|
126%
|
Midway Bus Upgrade
|
|
Copus-Lakeview 70 kV
|
163%
|
126%
|
Midway Bus Upgrade / Continue to monitor
|
|
Kern-Magunden-Witco 115 kV
|
132%
|
116%
|
Under Review / Sensitivity Only
|
|
Midway-Gates 230 kV
|
131%
|
141%
|
Under Review
|
|
Midway-Tupman-Rio Bravo-Renfro 115 kV
|
129%
|
132%
|
Midway Bus Upgrade
|
|
Famoso-Lerdo 115 kV
|
128%
|
123%
|
Midway Bus Upgrade
|
|
Semitropic-Famoso 115 kV
|
126%
|
129%
|
Under Review / Midway Bus Upgrade
|
|
San Luis Obispo-Carrizo 115 kV
|
126%
|
—
|
Continue to monitor
|
|
Lerdo-Kern Oil-7th Standard 115 kV
|
124%
|
113%
|
Under Review
|
|
Buena Vista-Midway #2 230 kV
|
119%
|
104%
|
Continue to monitor / Wheeler Ridge Junction
|
|
Kern-Stockdale-Lamont 115 kV
|
116%
|
110%
|
Under Review
|
|
Wheeler Ridge-Lakeview 70 kV
|
116%
|
120%
|
Under Review
|
|
Kern PP-Westpark #1 115 kV
|
111%
|
113%
|
Under Review
|
|
Fellows-Taft 115 kV
|
—
|
—
|
Sensitivity Only
|
|
Fellows-Midsun 115 kV
|
—
|
—
|
Sensitivity Only
|
Worst-case baseline is the highest loading recorded for the facility across the six baseline scenarios; a dash indicates no value at or above 100 percent in that column. Worst-case and High CEC values are frequently driven by different binding contingencies, and where a facility carries findings under more than one contingency, more than one disposition may apply. On the Kern-Magunden 70 kV contingency producing the 452 percent result, the 2031 Summer Peak case is recorded as non-converged. San Luis Obispo-Carrizo 115 kV appears in the PG&E Kern study area but is not located in Kern County. The first row on page 2 of the results carries no facility name and is treated here as a continuation of Lerdo-Kern Oil-7th Standard 115 kV from page 1; if so attributed, that facility’s 2031 High CEC value is 116 percent rather than 113 percent.
Table B-2. Low-voltage findings
|
Substation
|
Lowest p.u. (baseline)
|
2031 High CEC
|
Stated disposition
|
|
Tejon 70 kV
|
0.58
|
0.84
|
Sensitivity Only
|
|
San Bernard 70 kV
|
0.58
|
0.84
|
Sensitivity Only
|
|
Kern Ridge 115 kV
|
0.59
|
0.88
|
Continue to monitor / Under Review
|
|
Temblor 115 kV
|
0.59
|
—
|
Continue to monitor / Under Review
|
|
Wheeler Ridge 115 kV
|
0.59
|
—
|
Sensitivity Only
|
|
Wheeler Ridge 70 kV
|
0.59
|
—
|
Sensitivity Only
|
|
Magunden 70 kV
|
0.61
|
—
|
Tejon Area Reinforcement
|
|
Arvin 70 kV
|
0.63
|
0.87
|
Sensitivity Only
|
|
AE Victory 115 kV
|
0.82
|
—
|
Sensitivity Only
|
|
Midsun 115 kV
|
0.82
|
—
|
Sensitivity Only
|
|
Fellows G 115 kV
|
0.83
|
—
|
Sensitivity Only
|
|
Weedpatch 70 kV
|
0.84
|
—
|
Tejon Area Reinforcement
|
|
Wheeler Ridge 230 kV
|
0.85
|
—
|
Wheeler Ridge Junction
|
|
Kern Oil Junction 70 kV
|
0.85
|
0.85
|
Under Review
|
|
Fruitvale 70 kV
|
0.85
|
0.84
|
Under Review
|
|
Old River 70 kV
|
0.86
|
0.86
|
Under Review
|
|
Bakersfield 70 kV
|
0.87
|
0.86
|
Under Review
|
|
Cawelo B 70 kV
|
0.87
|
0.86
|
Under Review
|
Planning standard is 0.9 per unit. A dash indicates no reading below 0.9 per unit in that column. Substation names are given as they appear in the study results.
Table B-3. Transient stability findings
1. Internal fault at bus-tie breaker 302, Midway 115 kV Bus 1D; potential violation in the 2028 spring off-peak scenario; under review.
2. Internal fault at bus-tie breaker 392, Midway 115 kV Bus E; potential violation in the 2031 summer peak scenario; under review.
3. Fault on Midway-Wheeler Ridge 230 kV circuits 1 and 2; potential violations in all four baseline stability scenarios; no issues under either sensitivity; under review.
4. Failure of the non-redundant relay protecting the Westpark 115 kV substation bus; potential violations in the 2028 spring off-peak, 2031 and 2036 summer peak, and 2036 summer off-peak scenarios and in both sensitivities; mitigation identified (install redundant relay).
5. Failure of the non-redundant DC control circuit at Corcoran 115 kV circuit breaker 122; potential violations in the 2028 spring off-peak and 2031 summer peak scenarios; mitigation identified (install redundant battery supply).
6. Failure of the non-redundant DC battery supplying the Kern Oil substation 115 kV buses; potential violations in both sensitivity scenarios; dispositioned sensitivity only.
The transient stability assessment uses four baseline scenarios (2028 spring off-peak, 2031 summer peak, 2036 summer peak, and 2036 summer off-peak) and two sensitivities, a reduced set relative to the thermal and voltage assessments.
3.
Provide your organization's comments on PG&E's proposed reliability projects presentation
COMMENTS OF B3K PROSPERITY
V. REQUESTED PROJECTS AND SCOPING CONFIRMATIONS
The following requests are directed to projects and candidate mitigations already identified in the record of this cycle or the preceding one. B3K/AELAC does not propose a new transmission element in these comments.
1. Midway 115 kV Bus Upgrade
The Midway 115 kV Bus Upgrade was approved as a reliability-driven project in the 2025-2026 Transmission Plan (project 2526-R-08, PG&E, Kern area, estimated cost $44 million to $89 million, estimated in-service date May 2033). The preliminary results in the present cycle assign a further cluster of 70 kV and 115 kV findings to that project, including Taft-Maricopa 70 kV at 178 percent, Taft-Elk Hills 70 kV at 163 percent, Copus-Lakeview 70 kV at 163 percent, Midway-Tupman-Rio Bravo-Renfro 115 kV at 129 percent, and Famoso-Lerdo 115 kV at 128 percent. Two of these worsen under the high demand forecast relative to the 2031 baseline: Midway-Tupman-Rio Bravo-Renfro, from 129 to 132 percent, and Famoso-Lerdo, from 121 to 123 percent.
B3K/AELAC request that CAISO confirm whether the scope approved in May 2026 resolves the findings now assigned to it in this cycle, including under the 2031 high demand forecast; whether a scope change is required; and whether the May 2033 in-service date remains current, given that the findings assigned to the project bind in the 2028 and 2031 study years. B3K/AELAC further requests that CAISO clarify how reliability will be maintained prior to the project’s anticipated in-service date. If the approved scope is sized to a demand forecast that has since been superseded, B3K/AELAC requests that CAISO state whether the sizing basis will be revisited this cycle.
2. Wheeler Ridge Junction Mitigation
Wheeler Ridge Junction is named as the candidate mitigation for four separate Kern-area findings: Weedpatch-Magunden 70 kV at 195 percent; San Bernard-Weedpatch 70 kV at 325 percent under a P7 double-circuit tower line outage; Buena Vista-Midway #2 230 kV; and the Wheeler Ridge 230 kV low-voltage finding at 0.85 per unit. The same electrical area produces the Midway-Wheeler Ridge 230 kV transient stability finding, which appears in all four baseline stability scenarios. B3K/AELAC requests confirmation of scope and schedule, and requests that CAISO state whether this project resolves the associated stability finding and the unmitigated 334 percent P6 finding on the same facility.
3. Tejon Area Reinforcement
Tejon Area Reinforcement is named as the candidate mitigation for two low-voltage findings: Magunden 70 kV at 0.61 per unit and Weedpatch 70 kV at 0.84 per unit. Adjacent findings at Tejon 70 kV, San Bernard 70 kV (both 0.58 per unit) and Arvin 70 kV (0.63 per unit) are dispositioned as sensitivity-only. B3K/AELAC requests that CAISO state whether the reinforcement as scoped resolves those adjacent findings, and if not, what would.
4. Midway-Gates 230 kV Mitigation
Midway-Gates 230 kV is one of the most demand-sensitive facilities in the Kern-area results, at 131 percent under the 2031 baseline and 141 percent under the 2031 high demand forecast, and it carries no selected mitigation. B3K/AELAC request that mitigation be identified in this cycle, and that the mitigation alternatives assessment consider the high demand forecast case.
5. Path 15 and Path 26 Deferred Engineering Analysis
In the Board-approved 2025-2026 Transmission Plan, CAISO states that "this transmission plan has identified and confirmed the need for new additional transmission on the 500 kV corridor in the San Joaquin Valley, encompassing the Path 15 corridor and portions of Path 26," and that "[T]he ISO has identified a preferred option to meet these needs, extending as far north as Tesla and south to Midway and Windhub." CAISO further states that "Given the magnitude and impact on the 500 kV backbone grid, the ISO has identified the need for additional engineering details to be completed before a functional specification can be completed and a competitive process launched, so the ISO plans to seek Board of Governors approval and move forward with transmission reinforcement in the 2026-2027 transmission planning cycle."
The Plan identifies that preferred option as Alternative 6, consisting of the Gates-Los Banos #3 500 kV series compensation together with a new Windhub-Tesla 500 kV line tying the Midway and Gates 500 kV substations. CAISO records that this alternative "had the highest benefit to cost ratios among all remaining alternatives and is considered the most economically favorable alternative in longer term," at an estimated total cost of $3,271 million, and that "[t]he ISO is planning to recommend this alternative for approval in the next planning cycle after conducting bulk system reliability assessment by modeling this alternative to confirm if there is any impact on the bulk system." For Path 26, CAISO indicated it would further assess the feasibility of a remedial action scheme for south-to-north flows under the common corridor outage of the Midway-Vincent 500 kV lines.
The southern terminals of the preferred option, Midway and Windhub, are both in Kern County. B3K/AELAC accordingly request that CAISO confirm, in this cycle: (a) the schedule on which the bulk system reliability assessment and additional engineering for Alternative 6 will be completed; (b) when CAISO expects to seek Board of Governors approval, and whether that remains within the 2026-2027 cycle; (c) how the Midway and Windhub terminal configurations will be scoped in the functional specification, including any 115 kV and 230 kV terminal work at Midway that would bear on the local findings discussed in Section IV of these comments; and (d) whether the benefit-to-cost showing for Alternative 6 depends on adoption of a revised congestion revenue allocation approach, and if so, the schedule for that determination.
4.
Provide your organization's comments on SCE proposed reliability projects presentation
5.
Provide your organization's comments on GLW proposed reliability projects presentation
6.
Provide your organization's comments on SDG&E proposed reliability projects presentation
7.
Provide your organization’s comments on the high voltage TAC update
8.
Provide your organization’s comments on the policy assessment update.
9.
Provide your organization's comments on the economic assessment update.
10.
Provide your organization's comments on the Energy-Only Resources Assessment Preliminary Findings discussion.
11.
Provide any additional comments your organization has on the Sept. 23-24 2026-2027 Transmission Planning Process Meetings.