1.
                                            
                                            Please provide your organization’s comments on the ISO’s proposed recommendation regarding the Southwest Intertie Project – North.
                                        
                                        
The Public Advocates Office at the California Public Utilities Commission (Cal Advocates) provides these comments on the proposed funding agreement for the Southwest Intertie Project-North (SWIP-North) and the presentation on the proposed agreement on November 7, 2023.   Cal Advocates is an independent ratepayer advocate with a mandate to obtain the lowest possible rates for utility services, consistent with reliable and safe service levels, and the state’s environmental goals.[1]   
Background
The SWIP-North transmission project is a proposed 500 kilovolt (kV) transmission line that would connect the Idaho Power Midpoint substation with the NV Energy Robinson Summit substation and the existing One Nevada Transmission Line (ON-Line) in Nevada.[2]  As proposed, SWIP-North will be approximately 285 miles in length and have approximately 2,100 megawatts (MW) of transmission capacity.  NV Energy has already secured entitlements for approximately 1,000 MW of this capacity.[3] 
SWIP-North Benefit Analysis 
LS Power, the SWIP-North developer, claims that SWIP-North will have the following benefits.
	- It will improve the transfer capability between CAISO, PacifiCorp, NV Energy, Idaho Power, and Bonneville Power Association.[4] 
- It will increase Energy Imbalance Market benefits.[5]
- It helps meet west wide renewable portfolio standards (RPS) and greenhouse gas (GHG) goals.[6]
- It will enhance system reliability for the entire western Grid.[7] 
Proposed Funding Agreement for SWIP-North
As proposed, CAISO would acquire approximately 1,000 MW of transmission capacity entitlements (entitlements) on the SWIP-North and ON-Line in the north to south direction and approximately 500 MW in the south to north direction.  Idaho Power would pursue the remaining available 500 MW of entitlements in the south to north direction on SWIP-North.  The current project cost estimate is $1,090 million or $3.8 million per mile for SWIP-North and the necessary upgrades to the existing ON-Line project.[8]  Combined, these projects could provide California 1,000 MW of transmission capacity between the Midpoint substation in Idaho and the Harry Allen substation in Nevada.[9]  California already owns transmission capacity between the Harry Allen substation in Nevada and the California transmission system to accommodate 1,000 MW of Idaho wind.
Concerns
Cal Advocates supports CAISO’s pursuit of options to reduce the costs and risks for new transmission development out-of-state to meet California’s clean energy targets.  Cal Advocates appreciates that the proposed agreement is contingent upon the Idaho Public Utilities Commission’s approval of Idaho Power’s proposed interest in SWIP-North.[10],[11]  Cal Advocates has concerns regarding the capacity proposed for California versus other options that are consistent with cost causation, available wind resources in Idaho, and the lack of a project cost cap.  While SWIP-North is permitted, there is still uncertainty on whether the project timing and alignment are the most optimal and cost-efficient for the western interconnection and for California ratepayers. 
Proposed SWIP-North Capacity for California ratepayers
As mentioned, CAISO proposes acquiring entitlements on the SWIP-North and ON-Line equal to approximately 1,000 MW in the north to south direction and approximately 500 MW in the south to north direction.  During the November 7, 2023 SWIP-North proposal meeting, CAISO confirmed that the proposed project entitlements are based on the proposed Idaho wind procurement in California’s integrated resource planning (IRP) proceeding resource portfolio for study in the 2024-2025 CAISO transmission planning process (TPP).[12]   To access Idaho wind, CAISO would need to secure entitlements for only SWIP North and ON-Line capacity in the north to south direction.  Thus, it is unclear that there is a need for proposed entitlements for 500 MW of SWIP-North and ON-Line capacity in the south to north direction.  For this reason, Cal Advocates requests CAISO explain the reason for this proposed component of the agreement and its benefits to California ratepayers. 
Explore All Possible Funding Partnerships for SWIP-North and the proposed ON-Line upgrades.
Evaluate SWIP-North’s Transfer Capacity Benefits for the Northwest and Mountain Regions. 
Recently, the Federal Energy Regulatory Commission and the Joint Federal-State Task Force on Electric Transmission proposed that transmission planners consider the increased interregional transfer capacity a project provides in their transmission project selection and cost allocation processes.[13],[14]   In line with this recommendation, the Department of Energy (DOE) recently determined that under medium and high growth scenarios there is a need to increase the transfer capacity between the Northwest region where BPA and Idaho are located and Mountain region where Nevada and PacifiCorp are located.[15]
With this new requirement and analysis from the federal government, BPA and PacifiCorp may now have a reason to consider SWIP-North to meet their interregional transfer capacity needs.  As mentioned SWIP-North could provide transfer capacity benefits to BPA and PacifiCorp per LS Power analysis.  SWIP North also has available transmission capacity that could benefit BPA and PacifiCorp that may not be needed to meet California’s clean energy targets.
Available Funding from Federal Agencies and or Utilities
There are additional funding sources that should be explored for the remaining 500 MW of SWIP-North capacity in the south to north direction.  In the 2022-2023 CAISO Transmission Plan, CAISO specified that DOE loan financing or grants are being considered for the SWIP-North’s anticipated “underutilized capacity.”[16]  Recently, the Western States Transmission Initiative recommended that the Committee on Regional Electric Power Corporation (CREPC) and the DOE encourage BPA to finance and build additional transmission projects in the western interconnection.[17]  Given these potential sources of funding, LS Power should provide an update on its application for DOE funding resources. 
Confirm the Available Wind Resources at the Midpoint Substation in Idaho
Cal Advocates notes that in the last five years several significant wind generation projects withdrew or were suspended in Idaho Power’s interconnection queue.[18]  For this reason, Cal Advocates requests CAISO confirm the wind capacity that would be available at the terminus of SWIP-North, which is the Midpoint substation, for California Load Serving Entities to purchase should this SWIP-North funding agreement move forward.
Lack of a Project Cost Cap
During CAISO’s 2021 Transmission Planning Process, CAISO presented only the costs of SWIP-North in its analysis on the costs of accessing Idaho wind.[19]  The cost presented was $636 million in 2020 dollars for SWIP-North only.  The current proposal is for California ratepayers to pay approximately $842 million to access 1,000 MW of Idaho wind through the SWIP-North project and ON-Line upgrades.  Given this more than 30% cost increase, Cal Advocates recommends a project cost cap be established prior to final approval.
Summary of Recommendations and Requests
	- CAISO Should Explain How California Ratepayers Benefit from Having 500 MW of Transmission Capacity in the South to North direction on SWIP-North and ON-Line.
Cal Advocates requests confirmation that California would benefit from having 500 MW of south to north capacity through SWIP-North and ON-Line upgrades as proposed.  It appears that California may only need transmission capacity between Idaho and California in the north to south direction to meet its clean energy targets by 2035 and 2045.
If California ratepayers would not benefit from 500 MW of transmission capacity in the south to north direction on SWIP-North and ON-Line, CAISO should reduce its project participation in the south to north direction accordingly.
	- Explore Additional Funding Partnerships for SWIP-North and the proposed ON-line upgrades.
Transfer Capacity Benefit Evaluation
LS Power has also already determined that SWIP North would provide transfer capacity benefits to Bonneville Power Association (BPA) and PacifiCorp.  BPA and PacifiCorp may be required to consider SWIP-North for these benefits in their next planning cycle.  Cal Advocates supports this additional evaluation to confirm the proposed SWIP-North cost allocation is consistent with the expected benefits to the Balancing Authority Areas in the western interconnection. 
	- Confirm the Available Wind Resource Capacity at the Midpoint Substation for California. 
CAISO should confirm the wind generation projects in Idaho that will move forward and have available wind capacity for California before approving this proposed SWIP-North funding agreement.
	- CAISO Should Require a Project Cost Cap and Project Cost Review similar to practices in Southwest Power Pool.
Cal Advocates recommends two additional funding agreement contingencies, which are as follows:
	- SWIP-North and the proposed ON-Line upgrades should be subject to a binding project cost cap.
- SWIP-North and the proposed ON-Line upgrades should be subject to a project cost review to ensure ratepayers are only obligated for the established transmission capacity entitlement cost in an approved project funding agreement.  The main components of this project cost review would be:
	- Quarterly project cost updates;
- Project reevaluation if the project cost exceeds 10% of the approved cost; and
- The option for California to suspend or cancel its funding agreement if the project exceeds 20% of its approved costs.  This proposed project cost review recommendation is consistent with Southwest Power Pool’s existing project review process.  SPP’s project cost review process has assisted with keeping project costs at or below their original cost estimates.[20],[21] 
 
[1] Cal. Pub. Util. Code, § 309.5.
[2] ON-Line is owned by NV Energy and runs south between the Robinson Summitt substation and the Harry Allend Substation.  The Harry Allen substation in Nevada connects to the CAISO owned Desert Link line which terminates at the California- Nevada border at the Eldorado substation.
[3] Southwest Intertie Project (SWIP) North, Overview of March 2016 ITP Submissions to CAISO, NTTG & WestConnect, LS Power (Presentation), slide 5.
[4] Southwest Intertie Project (SWIP) North, Overview of March 2016 ITP Submissions to CAISO, NTTG & WestConnect, LS Power (Presentation), slide 11.
[5] Southwest Intertie Project (SWIP) North, Overview of March 2016 ITP Submissions to CAISO, NTTG & WestConnect, LS Power (Presentation), slide 11.
[6] Southwest Intertie Project (SWIP) North, Overview of March 2016 ITP Submissions to CAISO, NTTG & WestConnect, LS Power (Presentation), slide 11.
[7] 2018-2019 Interregional Transmission Coordination – Interregional Transmission Project Submittal, Great Basin Transmission ITP Submission to California ISO presentation (SWIP-North), May 2018, slide 6.
[8] CAISO 2022-2023 TPP: SWIP North Stakeholder Meeting, November 7, 2023 at p. 11.
[9] CAISO 2022-2023 TPP: SWIP North Stakeholder Meeting, November 7, 2023 at p. 11.
[10] CAISO 2022-2023 TPP: SWIP North Stakeholder Meeting, November 7, 2023 at p. 12.
[11] Idaho Power Letter on the Southwest Interties Project North to the President and CEO of the California ISO, November 1, 2023 at p. 2.
[12] CAISO 2022-2023 TPP: SWIP North Stakeholder Meeting, November 7, 2023 at p. 3.  California has not approved the proposed 2024-2025 resource portfolio yet. 
[13] Federal Energy Regulatory Commission, Staff-Led Workshop on Establishing Interregional Transfer Capability Transmission Planning and Cost Allocation Requirements, December 6, 2022 at https://www.ferc.gov/news-events/events/staff-led-workshop-establishing-interregional-transfer-capability-transmission
[14] Second Meeting of the Joint Federal-State Task Force on Electric Transmission, February 16, 2022, Docket No. AD21-15, Transcript statements from FERC Commissioner Christie at pp. 43-44 and NARUC Chair Scripps at pp. 74 and 130.
[15]  U.S. Department of Energy National Transmission Needs Study, October 2023 at pp. 137-138.
[16] CAISO Board Approved 2022-2023 Transmission Plan, May 18, 2023 at p. 102.
[17] Recommendations from Gridwork’s Western States Transmission Initiative, October 2023 a p. 5.
[18] Idaho Power Generation Interconnection Queue, Open Access Same-Time Information System (OASIS) site as of November 14, 2023 at http://www.oatioasis.com/ipco/index.html.
[19] 2021-2022 Transmission Plan, CAISO, March 17, 2022 at p. 305.
[20] SPP Open Access Tariff Business Practices at spp oatt business practices.pdf.  Refer to Section 5. Acceptance of an NTC-C or NTC 5.1.
[21]  Statement of Paul Suskie at the FERC Technical Conference on Transmission Planning and Cost Management. Docket No. AD22-8-000. Lines 14-18 on page 188 of the transcript.