LSA understands the CAISO’s objectives of limiting projects accepted for study to realistic levels, focusing on the most-ready projects, and we have long supported measures to remove non-viable projects from the queue. Our comments here support those overall objectives, and the significant progress that has been made.
However, we still have concerns with many details of this complex proposal. LSA’s comments do not cover all its concerns with the Final Proposal (Proposal), or (except where indicated) repeat its past comment submittals. Instead, LSA’s comments here focus on significant issues and/or new elements of the Proposal that should be addressed before it is made final.
OVERALL PROCESS AND SCHEDULE GOING FORWARD
LSA believes that consideration of the Proposal should be delayed to at least the July Board meeting (and perhaps October), and filed together with the Track 3 proposals. CAISO staff has worked hard, but still the Final Proposal reads more like a Revised Draft Final Proposal, i.e.:
- The Zonal concept still contains significant unclarities and inequities (and potentially problematic results following the current TPD Allocation cycle);
- Many proposed elements cannot be fairly applied to Cluster 15, even if they might be appropriate for later clusters;
- The proposal contains significant new elements (e.g., Energy Only proposals) that have not been sufficiently considered or vetted; and
- The interactions between the Intake and Queue Management proposals here and the TPD Allocation process cannot be determined with the deferral of rules for the latter to Track 3, and the CAISO should consider putting the final proposals for both tracks into a single package.
SUMMARY OF COMMENTS
- Zonal framework: Additional clarifications, and consideration of inequities and potential adverse TPD Allocation impacts, are needed.
- Energy Only proposals: Additional clarifications and details, and consideration of inequities, are needed.
- Zonal-level Scoping Meetings: Should be supplemented by a means for Interconnection Customers (ICs) to pose questions about their projects on a confidential basis.
- Commercial Interest: Should be deferred to Cluster 16. If retained:
- The points weighting should be decreased significantly, since they will otherwise determine which projects are studied, and LSEs themselves have not had sufficient time to implement fair and open project selection methods;
- The Self-Build and Full Allocation options should be modified, to prevent limitations on open access and competition and “crowding out” of more-viable projects; and
- The non-LSE interest element should be clarified and modified.
- The Engineering Design Completeness element should better define the “percent complete” status markers.
- The elements related to facility expansion should: (1) include projects that have not yet started construction but have progressed significantly along that path; (2) apply to projects that have interconnected in a variety of study paths (e.g., WDAT); and (3) clarify that the parties owning the original project and the expansion need not be the same.
- Additional elements should be considered, such as developer experience and equipment procurement.
- System Need – Local Capacity Area (LCA): The CAISO should clarify whether potential charging limitations will impact awards of these points, and if so, how that will be done.
- MD projects – use of Commercial Readiness Deposit forfeits: Because these deposits are provided specifically by Merchant Development Zone projects to fund ADNUs, they should be divided among any remaining projects sharing that ADNU instead of being diluted through the normal forfeited-funds process.
COMMENT DETAILS
ZONAL FRAMEWORK OVERALL
LSA appreciates the many clarifications and explanations provided at the April 4th stakeholder meeting about Transmission Plan Deliverability (TPD) Zones vs. Merchant Deliverability (MD) Zones. However, there are still some definitional unclarities, as well as some apparent inequities, in the zonal framework as described.
Unclarities
The terms “zones” and “constraints” need to be better defined. It appears that “zones” are defined by larger constraints and the term “constraints” means inter-zonal constraints, but that is not clear.
In particular, the TPD-MD zonal distinction of “at least 50MW of available capacity” is not at all clear. For example:
- Is the 50MW limit the total of capacity behind all intra-zonal constraints within a zone? The CAISO said at the last stakeholder meeting that the available capacity behind the intrazonal constraints was not necessarily additive, but then how is the zonal capacity determined?
- How is available capacity behind zonal and intra-zonal constraints allocated to specific POIs?
In addition, LSA is very concerned about the impact of the current TPD Allocation cycle results, especially with respect to from the very large Cluster 14 group. The Proposal states that the CAISO did a kind of “dry run” on the available Cluster 15 data and determined that about 200 (of 500+) projects were located in TPD Zones, and 112 would be accepted for study.
However, it seems a distinct possibility that many or most zones now shown as having available capacity currently will not have it after the TPD Allocation is complete, e.g., all or nearly all zones will be defined as MD Zones, and many projects in remaining TPD Zones but at POIs without available capacity will be disqualified from study (see more below).
Is there a minimum number of projects, or amount of capacity, below which the CAISO might reconsider this framework? For example, if only, say, 40 or 50 projects can be accommodated in remaining TPD Zones, will the CAISO consider that to be an acceptable result? The CAISO should consider defining a minimum amount of capacity or projects to be accepted for study under TPD Zone rules to avoid an undesirable outcome.
Inequities
There are inequities embedded in the zonal grouping of POIs and constraints into TPD Zones vs. MD Zones. Further, some elements that may be fair for later clusters – which will have the benefit of the consolidated and enhanced information packages the CAISO is starting to develop, perhaps six months before they submit their Interconnection Requests – may not be fair to apply to Cluster 15 projects, which did not receive this useful information so far in advance (and still do not have updated information due to the need for updates after the current TPD Allocation cycle).
The zonal framework generally would impose a major inequity on TPD Zone projects seeking interconnection and deliverability at POIs behind sub-zonal constraints. Factually, these projects would be in the same situation as projects seeking interconnection and deliverability in MD Zones (i.e., no deliverability currently available at their locations), but they would receive worse treatment – they won’t be studied, no matter how high their viability scores, and (unlike MD Zone projects seeking deliverability), they would have no option to fund even reasonable-cost ADNUs (perhaps more reasonable-cost ADNUs than in MD Zones).
The inequities for projects in this situation are compounded for Cluster 15 projects. Developers submitting projects in future clusters will have the benefit of the aforementioned advance information and can avoid POIs in TPD Zones without available deliverability, but C15 projects did not have that advance information.
LSA understands that the CAISO strongly desires to reduce the number of Cluster 15 projects studied to a workable number, and excluding projects at POIs in TPD Zones without deliverability would help achieve that goal. However, it would fairer and more equitable to allow these C15 projects a one-time pass and use an MD option in this cycle.
ENERGY-ONLY PROJECT PROVISIONS - ZONES WITHOUT CPUC IRP BASE-PORTFOLIO CAPACITY NEED
The proposals related to EO projects are brand new in the Proposal, and thus there has only been limited opportunity for meaningful consideration. LSA has several concerns about these proposals.
First, the EO zones will be defined by the presence or absence of deliverability, when EO need has nothing to do with deliverability. There is no particular reason why those zonal definitions should apply to EO projects.
Second, this proposal is not fully fleshed out. For example, would EO projects at busses in zones where the CPUC IRP base portfolio indicates an EO resource need (call them “EO Reimbursement Zones”) also apply at the POI level, i.e., would projects at POIs within EO Reimbursement Zones where there is no CPUC EO need shown still have an RNU Reimbursement Option?
Third, this proposal has inequities also. In particular, LSA is concerned that EO projects seeking interconnection in MD Zones showing no CPUC EO need would receive no RNU reimbursement, while projects seeking interconnection and deliverability within such zones would receive reimbursement for both RNU and LDNU costs.
In both situations, the projects are seeking interconnection in areas without indications of need in CPUC portfolios, and there is no basis for treating them different with respect to RNU costs. If projects seeking deliverability in areas without a portfolio need would qualify for RNU refunds, then so should EO projects seeking interconnection only under the same circumstances.
Again, there are particular inequities concerning Cluster 15 timing, where developers did not have the same consolidated and enhanced information before IR submittal that will be available in advance for future clusters. There certainly was no advance notice that the CPUC IRP base portfolio would be used for this purpose.
ZONAL-LEVEL SCOPING MEETINGS
LSA is concerned that frank discussions about confidential individual project details that now occur in Scoping Meetings won’t take place in the proposed zonal-level Scoping Meetings. LSA urges CAISO to implement a supplemental process (e.g., Q&A in writing) for project-specific details needed by developers to make POI and other critical post-meeting decisions.
SCORING RUBRIC
Commercial Interest category - LSE points: LSA continues to share the significant reservations expressed by TerraGen and others about this element of the scoring rubric.
Disproportionate weight
Most projects (and especially most solar and wind projects) will not qualify for points under the System Need category (Local Capacity Area location or long-lead-time technologies). Thus, most projects can qualify for a maximum of only 65 points – 30 for Commercial Interest (off-taker need (mainly LSE)) and 35 for Project Viability.
Thus, nearly half of the possible points for most projects will be based on Commercial Readiness, where LSE interest points carry a weight four times non-LSE interest points. It seems almost unavoidable that this element will therefore be the deciding factor determining which projects are accepted for study, a result that large numbers of stakeholders (and the CAISO itself) have said should be avoided.
The problem is compounded by the timing of this initial implementation. While the CAISO encourages LSEs to modify their tariffs to provide for open solicitations, with fair and transparent project selection and points allocation processes, there is not enough time for those processes to be applied to Cluster 15 between the time when zones are defined as TPD or MD (perhaps in July) and the December LSE points allocations.
This proposal could thus potentially exclude highly viable projects, through non-transparent, unclear, and potentially uncompetitive LSE processes.
LSE self-builds
This is a particular concern given the new proposed rules for LSE designation of self-build projects, allowing such designations for the greater of three projects or 25% of an LSE’s allocation points. It is not hard to envision at least some LSEs designating three large self-build projects that would meet all of their needs and short-circuiting the competitive process entirely.
Full Allocation option
LSA is also concerned about removal of the 150% of need limitation for the Full Allocation option, allowing small LSEs to designate large projects many times their actual resource need. There is little justification for this proposal – resources supported by only small LSEs can downsize like other projects if they do not receive interest from other LSEs, so they would still qualify for the full number of weighted points and be able to support the load needs of the small LSE. They could also seek interest from non-LSEs.
It would certainly distort the process if very small LSEs could use this election (e.g., a 10MW LSE supporting a 100-200MW resource) to crowd out otherwise higher-scoring resources. If such LSEs can extend their points allocation to resources that exceed their need by such large amounts, then the additional capacity accepted as a result should not be allowed to exclude other viable resources, i.e., it should not count toward the 150% limit.
Applicability to Cluster 15
Like other elements of the scoring rubric, this category has the potential to be even more unfair if applied to C15, where even LSEs wanting to apply competitive processes will be severely limited given the timing.
LSA understands that CAISO wants encourage a system where LSEs conduct significant solicitation activities before IRs are submitted; the Proposal urges them to make tariff and process changes to accommodate project assessments much earlier in the process. However, those before-submittal tariff changes and preliminary activities did not happen for Cluster 15; in fact, LSA member discussions with LSEs has indicated considerable confusion and concern about how those entities will be able to make those judgments in the few months remaining before scoring-rubric application.
Conclusion
LSA urges the CAISO to focus on strengthening the Project Viability category elements (see below), and defer consideration of Commercial Interest preference elements to future clusters, once experience is gained with Cluster 15 and LSEs have the opportunity for rational pre-IR implementation of open and transparent project-assessment processes. It will be a long time before the Cluster 16 application window opens, and the CAISO can use information gained from the Cluster 15 process to refine and revise this approach considering the systems that LSEs have put in place by then.
If the CAISO nevertheless retains the Commercial Interest element for Cluster 15, to ensure that the most viable Cluster 15 projects are retained and studied, it should:
- Reduce LSE/non-LSE points weighting from 30 points to 10 points for Cluster 15;
- Reduce LSE ability to designate self-build projects to the lower of three projects or 25% of their points total, instead of the greater of those two measures; and
- Restore the 150% of need limit for LSEs using the Full Allocation option, or at least exclude capacity beyond 150% of that LSE’s points allocation from the zonal 150% capacity limit.
Commercial Interest category - non-LSE points
As noted above, LSA believes that the entire Commercial Interest category (including this element) should be deferred, or at least carry a reduced weight, consistent with its above views on LSE interest.
If the Commercial Interest category is retained, then the CAISO should revisit some of the restrictions proposed for non-LSE expressions of interest, specifically:
- Limit of one project per cycle: Non-LSEs with large and dispersed loads would be restricted to only one project,like those with small and more localized loads. Commercial entities should be able to designate projects in a manner that reflects their needs, not only by capacity (e.g., the attestation required that the designation reflects the size of their needs) but also location, e.g., choosing a larger number of smaller projects over a single very large project.
- Purpose of non-LSE procurement: The CAISO should not concern itself with the purpose of non-LSE procurement, which could reflect multiple legitimate corporate objectives besides “corporate sustainability policy goals.” For example, a non-LSE could want to ensure a reliable local supply of energy or economic development in areas where it has facilities (an objective shared by LSEs like NCPA and some CCAs). The CAISO should not
- Market offers for deliverability: To ensure that any deliverability awarded to projects endorsed by non-LSEs is available to the market, the CAISO can include in the required affidavits an attestation pledging to offer RA provided by projects eventually contracted to LSEs or entities selling RA to LSEs.
- The CAISO should better define which entities qualify as “non-LSEs.” For example, is this category limited to commercial/industrial end-users with facilities in the CAISO area? Would municipal governments or residential customers qualify?
Project Viability category - engineering design completion
LSA is concerned that this criterion will be simply a “pay to play” requirement, i.e., will favor those willing to lay out money for the work, and not necessarily a genuine measure of project viability.
In addition, while most LSA members have significant and wide-ranging experience designing and building generation and storage projects, we are puzzled by the “engineering design plan completeness” criterion. The CAISO should provide more detail as to what constitutes “10% completion,” “20% completion,” and so on, and add a requirement that the work must be specific *to the site, in order to add clarity to this process.
The CAISO should also consider adding a requirement that the certifying engineer be from an independent company.
Project Viability category - “facility expansion”
The current proposal would award points for: (1) Expansion of facility in operation/under construction where existing Gen-Tie can accommodate the new resource, 50 points; (2) expansion of operating facility, 20 points; or (3) expansion of facility under construction, 10 points.
LSA suggests one modification and two clarifications to this criterion.
The modification is an additional category (e.g., 5 points) for expansion of a facility that is in the queue and clearly moving ahead but is not yet under construction, e.g., that has: (1) made its second postings; and (2) executed GIAs and is in good standing with those agreements. This change would recognize that sharing of facilities between projects in the queue would tend to increase the financial and other viability of both projects. It could also help in adding points variations and avoiding tie scores.
The two clarifications are as follows.
- The “existing facility” under construction or operational (or, per LSA’s suggestion above, in the queue and moving ahead) should include those under any type of interconnection arrangement, e.g., WDAT, Rule 23, QF, behind-the-meter, etc.; because:
- There is no restriction in the Proposal on the definition of an “existing facility.”
- Facility expansion effectively is a stand-in for “more cost-effective,” “needing fewer Interconnection Facilities,” “more likely to be permitted,” “built by an entity that knew how to make it happen,” and other factors. That would be true regardless of the voltage level or interconnection contract form of the facility being expanded.
- The developer of the expansion facilities need not be the owner of the original facility. The CAISO said that at the stakeholder meeting that it would treat this situation the same as the current rules for project IRs proposing to share gen-ties owned by others, i.e., IRs with a demonstration that an arrangement is under negotiation, and later provision of an agreement.
Project Viability Category – other possible measures
LSA is concerned that the proposed measures in the Project Viability category will result in a large number of scoring ties, making the Commercial Interest (primarily from LSEs) the main determinant of which projects are accepted for study. Another way to mitigate this effect (aside from the Commercial Interest revisions suggested by LSA above) is to add more criteria to this category. Below are some measures suggested by LSA earlier in this process.
- Overall developer experience/success at bringing on-line and/or operating projects of the technology type and size of the proposed projects, similar to that element in the CPUC “RPS Project Viability Calculator” (https://www.cpuc.ca.gov/search#q=%22viability%20calculator%22&sort=relevancy). That scoring measure counts by the CPUC for up to 25% of a project viability score, with “project development experience” weighted to 20% and “ownership/O&M experience” worth up to 5%.
This broad experiential measure would capture, not only productive relationships with vendors, but also overall competent and experienced project construction skills and operating experience.
The CAISO said earlier that this assessment would be too subjective and difficult to validate, but any major market procurement of significant import would at least consider the experience and skill of the supplier. LSA suggests that the CAISO check with the CPUC and PTOs to see how that factor has been applied in the Viability Calculator process before dismissing it as unworkable.
- Master Service Agreement, Engineering/Procurement/Construction (EPC) agreement with equipment included, or similar purchase arrangement for major equipment, such as transformers, inverters, and/or key technology-specific equipment, with extra points for a demonstration that the equipment is specific to the site or project.
System Need - Local Capacity Area (LCA) charging limitations
The CAISO should clarify how LCA charging limitations would be applied to storage capacity in the scoring/intake process. The CAISO said at the stakeholder meeting that those limitations were not in the Final Proposal, then there was a discussion about whether those limitations might in fact be imposed, then there was confusion over whether the CAISO might impose a 100% or 150% limit. It was clear that this important issue had not yet been considered in depth by the CAISO, and the final framework should contain clear rules about the process to be used.
MD PROJECTS - USE OF COMMERCIAL READINESS DEPOSIT FORRFEITS
The Proposal would require MD projects seeking deliverability tot provide a Commercial Readiness Deposit of:
- 5% of estimated ADNU costs with their Interconnection Requests, or $10K/MW if no estimates are available ($500K min./$5M max., 50% non-refundable after IR validation completion); and
- 50% of estimated ADNU costs after cluster-study completion, 50% non-refundable. The deposit “will be a portion of the overall funding used by the PTO to construct the ADNU” and thus will not be refundable after COD.
The Proposal says that any forfeits of these postings would be treated like any forfeits today under GIDAP, i.e., per GIDAP Section 7.6. Section 7.6 allocates forfeited security amounts to reduce the cost to remaining projects for still-needed Network Upgrades proportional to the share of Current Cost Responsibility (CCR) accounted for each upgrade.
The problem is that, due to the ADNU posting requirements above – which are due in higher proportion earlier than postings for other upgrades – the proportion of the posted (and thus) forfeited security when a project withdraws that would be accounted for by ADNU costs would be higher than the CCR proportion. In other words, Section 7.6 is only fair when the postings for the different upgrades are proportionate, which would not be the case for ADNUs under the Proposal.
Thus, Section 7.6 should be revised to provide that forfeited security posted separately and specifically as Commercial Readiness Deposits for ADNUs should be used to reduce the ADNU costs allocated to remaining projects sharing the ADNU costs, which must now assume the cost share no longer covered by the withdrawing project.
3.
The ISO is seeking stakeholder feedback on the effectiveness of its recently adopted working group process and its overall contributions to the IPE 2023 proposal development process. We would greatly appreciate your responses to the following survey by end of day April 18, 2024: https://www.surveymonkey.com/r/YHWNWC2